.... in theory, if you run the battery completely flat. Personally, I'd run it for no more than ~40mins.If the battery voltage is the same as the heater voltage, then one 25 amp-hour battery will run one heater for one hour.
That's a lot of battery power. Maybe consider a backup generator?Hi I have 10 heaters running at 25 amp each .
What rating lead acid batteries should I get if I want to run them for 1 hour ? In the case of a power shortage.
Thank you .
Definitely, backup generator. Car type batteries are not going to cut it. There are "power company" size batteries if you want to go that way. .Voltage is 415v 3 phase
Hi I have 10 heaters running at 25 amp each .
The above two entries can be deciphered as there are: 10 Heaters * 25A * 415V * 3 phases * 1 Hour ~ 311250 WH?Voltage is 415v 3 phase
You don't multiply by 3 phases to get the power, so the value is 1/3 of your calculated value.The above two entries can be deciphered as there are: 10 Heaters * 25A * 415V * 3 phases * 1 Hour ~ 311250 WH?
What?You don't multiply by 3 phases to get the power, so the value is 1/3 of your calculated value.
The power is spread over the three phases.
100 kilowatts?
Might as well be jigg-a-watts. That's enough juice to run 10 to 20 households
My assumption was that it was 10 heaters total, each heating drawing 25A total, not per phase.What?
415 x 25 = 10375 watts per phase times three phases equals 31125 watts per heater times 10 heaters so,
415 x 25 x 3 x 10 = 311250 watts. Or it could be said that he has 30 415 volt 25 amp heaters spread over three phases rather than one.
.............