I have 415V , 200A 3 Phase wire system., Now i want to feed this inputs to a Controller which allows analog data of 0-20mA.
We can use control transformer (200A to 5A)+ Control transducer (5A to 0-20mA).

But these are costly as well as consuming lot of space.,
Is there any other way where i can get the desired outputs with minimal costs as well as space.
 

drc_567

Joined Dec 29, 2008
1,156
For your consideration ...
https://aimdynamics.com/product/333-mv-to-4-20-ma-transducer/
This device converts a millivolt AC signal to 4-20 ma. There is not anything shown that explains the 4 ma minimum value.
... It may be possible to shift the resulting output to a 0-16 ma range, if that is necessary.
... One additional component would be a toroid, or something similar, to link primary AC current flux to an AC millvolt signal.
... As you have pointed out, the project hinges on the economics.
 