Supply Frequency50/60Hz

Thread Starter

archxth_13

Joined Nov 23, 2021
24
Hello my fellow engineers

I am currently working on a project that requires me to use motors rated for a 60Hz supply and connect it to a 50Hz supply. Now as per my research I have come to realise that among other conditions, the motor will function at a lower speed and will thus require a higher power output to maintain the speed I would usually get on a 60Hz supply. My question is, is there a calculation that I could use to calculate the power required to maintain the same speed for the motor (rated for a 60Hz supply) when connected to a 50Hz supply.

Your advice will be highly appreciated.
 

Ian0

Joined Aug 7, 2020
13,097
What type of motor is it?
A universal motor will run off AC or DC so the frequency will make no difference.
A synchronous motor will run at synchronous speed regardless, so you’re stuck with 1500 rpm or 3000 rpm, depending on how many poles it has.
An induction motor cannot exceed synchronous speed, so will never go any faster than 1500/3000 rpm.
Your only option will be to increase the size of the pulley.
 

LowQCab

Joined Nov 6, 2012
5,101
Overall Horsepower-Output WILL BE REDUCED in any case,
and the propensity for overheating, even under "light-Loads",
will be increased by a very noticeable degree.

Make sure it stays well ventilated, and preferably even "cool".
.
.
.
 

crutschow

Joined Mar 14, 2008
38,316
Motors rated for 60Hz that are used on a 50Hz supply will likely overheat and not deliver their rated power.
Instead use motors rated for 50Hz.
They will then also generate their rated power (torque x RPM) at 60Hz, but at a 60/50 increase in speed for synchronous or inductions motors, which you will have to live with, possibly requiring a change in pulley diameter or different load (e.g. different fan or pump size for example).
AC motor speed is not readily adjusted other than by changing their operating frequency.

What load is the motor driving?
 
Last edited:

MaxHeadRoom

Joined Jul 18, 2013
30,557
Are these 3ph or 1ph motors?
In some cases where 1ph motors are used experiment with changing the run capacitor values can alleviate the slightly higher current that may occur.
 

Thread Starter

archxth_13

Joined Nov 23, 2021
24
So this is just a general conversation topic, Ill be using 3-phase motors for this particular exercise. I agree that the system will not be able to deliver enough power to the motor, but is there some calculation that could be used to find out how much power will be delivered?
 

MaxHeadRoom

Joined Jul 18, 2013
30,557
All Depends on the individual motor, You will find there are quite a few AC induction motors that have a 60/50 Hz rating, they can operate on either 60 Hz or 50 Hz power.
RPM will be lower and HP reduced by ~20%
 

Ian0

Joined Aug 7, 2020
13,097
It depends on how close to saturation of the magnetics it runs.
Just a thought. . . .
Considering that most 50Hz countries have 230V supplies, and most 60Hz countries have 120V supplies, a 60Hz motor on a 50Hz supply is probably running from a transformer. Reducing the voltage to 50/60 of the rated voltage will make it run at the same flux density as it was intended.
 

MisterBill2

Joined Jan 23, 2018
27,164
Hello my fellow engineers

I am currently working on a project that requires me to use motors rated for a 60Hz supply and connect it to a 50Hz supply. Now as per my research I have come to realise that among other conditions, the motor will function at a lower speed and will thus require a higher power output to maintain the speed I would usually get on a 60Hz supply. My question is, is there a calculation that I could use to calculate the power required to maintain the same speed for the motor (rated for a 60Hz supply) when connected to a 50Hz supply.

Your advice will be highly appreciated.
You WILL NOT GET the same speed running an induction motor at 50HZ instead of 60Hz.
 

MisterBill2

Joined Jan 23, 2018
27,164
The OP already stated he was aware of that in the his first post, you quoted ??
My response was in regard to this line in the post:
"My question is, is there a calculation that I could use to calculate the power required to maintain the same speed for the motor (rated for a 60Hz supply) when connected to a 50Hz supply. "
The work around, if it is a direct drive application, is to use a variable speed drive.
If there is any link, such as a belt or gearbox, then a simple ratio change would work.
 