Whatashame
- Joined Nov 30, 2015
- 88
And maybe the inspector will get crabs.Look at all the clams you'll find.
And maybe the inspector will get crabs.Look at all the clams you'll find.
I'm virtually 100% certain the sub panel main breaker can be anything. The one in the main panel does the wire protection anyway. A higher amperage breaker just becomes a disconnect. A lower amperage breaker "trips first". The important thing is to assure the wire is current limited by the breaker at the source end of the wire.I The sub panel main breaker has to be the same amperage or less than the breaker at the power source, not larger. If you make it less an advantage of this would be that the smaller breaker size will now trip first if there is a problem, like a short circuit or overload.
My understading is you can have to buy a kit to convert a "main breaker" panel to a sub-panel. The kit address the isolated neutral bar and you remove a jumper.
You can have a 200 A breaker in the sub, but the panel would be fused at the main panel say at 60 A. This is incorrect. A 200 amp breaker must be feed with 200 amp wire. Now, if you installed a 200 amp staight buss panel, (no main) then you might be able to get away with that. A 60amp sub panel should not have the ability to have 32 or 40 circuits. I think a 12 circuit panel for 60 amp would be best. I have never seen what you described, not that it hasn't been tried. Whatashame out
You do have to separate ground and neutral all the way back to the main panel.
Out buildings require a ground rod primarily for lightning. They don't get the ground/neutral bond.
The number of circuits and/or convenience determine whether you want a "main breaker" in the sub-panel.
No they can't. A main breaker must be fed with same amp wire as breaker indicates. Just lugs, and no breaker, maybe so.I'm virtually 100% certain the sub panel main breaker can be anything. The one in the main panel does the wire protection anyway. A higher amperage breaker just becomes a disconnect. A lower amperage breaker "trips first". The important thing is to assure the wire is current limited by the breaker at the source end of the wire.
You need the "kit" to convert a "main breaker" to a "sub-panel". The sub-panel w/o a breaker is known as a "Main Lug". It's a sub-panel by default.
Sub-panels have separate neutral and ground buses.
You can read the NEC online. I haven't done it in a while.
The "6" rule is what I remember.