single to 3 phase vfd cicuit

Thread Starter

jonnydolt

Joined Oct 23, 2015
145
Hi Guys thanks for reading.I have a 3 phase compressor with a 5.5kw motor,this will run on single phase via a 7.5kw vfd. I will need to run a whole new circuit but I also want to have an additional 15amp double gpo right next to it.Can this be done with 1 cable or will I need 2 ? and what size breaker/'s, cable/'s and gpo's would you use? The cable length will be 10 meters from the meter box to the power points and run in conduit 240 volts
 
Last edited:

MaxHeadRoom

Joined Jul 18, 2013
28,617
There must be local reg's that you can consult for your part of AU.
In N.A., this would Ideally be done with separate conductors/breakers etc.
Max.
 

jpanhalt

Joined Jan 18, 2008
11,087
A rotary phase converter ? aren't they bulky and really expensive ?The vfd is small and only $280.AU
Times have probably changed. I built mine in the 80's from a used 5 HP 3-phase motor. My situation was perhaps different. I had 3, 3-phase machines. So, the single converter just ran and I could run anything or combination of machines off it. I thought maybe you wanted a VFD to change speed, which I would not do with an air compressor.

I didn't realize that a 7.5 , continuous duty VFD was so cheap today.
 