Single phase 240v motor starter & overload with on/off switch wiring
designfoundry
Joined Feb 6, 2020
Hoping you all can help me wire up my single phase 240v induction motor. Can someone please explain or even better sketch out where the wires need to go, I have a fair idea already just want some good advice before I continue.
Switch is CK-5 10A 250v - SWITCH
Thanks in advance!
Dodgydave
Joined Jun 22, 2012
11,395
Put 95 and 96 in series with the stop button..
You might have to run the Live through L2, T2, L3 T3, in Series if it keeps tripping.20200206_143227.jpg
MaxHeadRoom
Joined Jul 18, 2013
30,836
Here is some control circuits. Table 3 page 4.
Also you can use also the NO O/L contacts 97-98 for e.g. indicator lamp as a warning a overload has occurred .
BTW, the attached PDF shows the O/L on the RH side of the contactor coil, it is now recommended to be placed in the control string in the left of the coil .
Your motor will be switch by the contactor L1.L2. L3.
Max.
MaxHeadRoom
Joined Jul 18, 2013
30,836
Here is a DWG for it, if using a 1ph motor then just one of the 3ph contacts used, although it is customary to take the 1ph conductor out of the bottom to the next top terminal and so on for all three, i.e. looped through.
This in order that the O/L senses on all its three input connections . As DodgyDave said.
Max.