Simple relay schematic question

Thread Starter

Etbrown44

Joined Aug 16, 2025
3
I've connected this simple time delay relay before, but need a tip this time as I'm not getting output.
I have 110v supplied to A1 and A2. I read nothing on 15,16 or 18, even after time delay has passed. It is a "delay on" relay.
I have 2 of these relays. One new. Both unlikely to be defective, so has to be operator error!
Suggestions most welcome.Screenshot_20250816_200732_Amazon Shopping.jpg
 

MisterBill2

Joined Jan 23, 2018
27,171
OK, understand that those terminals, 15, 16, and 18, are contacts and not outputs. #15 connects to #16 until the relay operates, then it connects to #18. So whatever you connect to #15 comes outof either #16 or #18.
The circuit shown in post #1 is very clear about that.
 

MisterBill2

Joined Jan 23, 2018
27,171
If the relay power is supposed to be A1 and A2, then there is a problem with the circuit shown in post #4. I think tyhat the connection to terminal A2 should go to the other side of the lamp.. As shown, when the lamp is switched ON, the timer power switches off., with both A1and A2 tied to the hot side.
 

Tonyr1084

Joined Sep 24, 2015
9,744
@panic mode Examine your diagram. A1 & A2 are AC power. Observe the Tilda ( ~ ) in the TS drawing.

Here's my take on this:

Before being set (below) Line is on pin 16. SET has not been "Set".
View attachment 354357
SET has been set (Next pic) and now Line is on pin 18. The load (light bulb) is energized.
View attachment 354358
After SET has been released (below), the relay continues to hold pin 18 hot for the pre-determined time period.
View attachment 354359
Once the time period has expired the system shuts the light off (below)
View attachment 354360
 
Last edited:

Tonyr1084

Joined Sep 24, 2015
9,744
It's on delay.
We supply hot side of 110v to 15 and it contacts 18 after the preset time.
Here's the modified drawings to match your description:
At rest. The light is off.
Pre SET.png


SET has been set (Next pic) Timing period begins. The light is still off.
View attachment 354393

SET has been released and the timing period has expired. The light comes on.
HOLD.png

My NEXT question for consideration is "How do you turn the light off?"
 

panic mode

Joined Oct 10, 2011
4,864
check timing diagram.
Un - Supply voltage (permament-ish...)
S - switch closure, timer start timing after S is off (including on power-up). then after time t output is energized.
R - relay output (NO). NC is opposite....

1755533431223.png
 

panic mode

Joined Oct 10, 2011
4,864
that is one option. the other is to turn switch on. both are clearly shown in the time diagram.
if different operation is wanted, just move lamp wire from NO to NC contact.
 

Tonyr1084

Joined Sep 24, 2015
9,744
I'm just wondering why you want to turn on a light, leave the room, then have the light come on after you've left? And we still don't know how the light is going to be shut off. And we're just assuming the load is a light. So let's ask the 64K dollar questions - what's the load? And why should it be delayed?
 