I am new here. I want a circuit diagram for tracing point of short circuit in a five core cable laid 1.2 metres underground and runs about 15 metres from a building to another. Please it is a shool assignment.
It would certainly be quite challenging - but perhaps a good illustration of the use of four-wire methods for low resistance measurement. If a four-terminal meter were unavailable, the next best thing might be to run a fairly substantial current around a pair the of shorted conductors, and measure the voltage drop with a reasonably sensitive voltmeter. Depending on the wire gauge, they should be able to get some tens of millivolts per loop metre with half an amp or so. Testing from both ends of the cable (if accessible) would help.Adjuster,
Point well taken; that's why I didn't mention FDR.
Resistance measurements could show which are shorted and/or open, but our OP's requirement stated that they needed to locate the point where the wiring is shorted.
Granted, they might be able to discern the distance (if the short is "perfect") by the resistance of the wire, but that would require a pretty accurate meter.
I agree with you.Perhaps they would need to follow that 555 by something to speed up the edges a bit. If they want to resolve to say 1 metre, wouldn't they need to get \(\leq\)10ns displayed rise time for the echo?
(Assuming cable velocity is about 2e8m/s, round trip delay is 10ns/metre?)
This may indicate the depth of interest.I want a circuit diagram
All viable methods were listed in post #12.thank you brothers for your concern. I studied the TDR but it is too advanced for me. Are there other ideas that would not require an oscilloscope? Since there is no power source around the track, what is required of me is a battery powered handheld detector.