Hi All,
I need to take some measurements of a 480VAC line using my Siglent SDS1204X-E. I was planning on using 3 channels measuring with respect to GND. My scope inputs say they tolerate 400Vpk. Our line runs hot at 495 VAC (rms), so If I measure relative to GND, I have 286 VAC (rms), which is 404 Vpk.
Now my probe is 10:1 so I get 40.4 Vpk at the scope input which is OK right?
Measuring this will not damage my scope?