Right way to calculate consumption
willhelmx
Joined Oct 3, 2022
Hi guy´s
What is the right way to calculate the below static 3-phase power consumtion in kW/h
We get 1 data measure/min -equal to 60 sets per Hr
Load is a 3-phas, voltage is phase a+b,b+c,c+a
Best Regards
/A
ericgibbs
Joined Jan 29, 2010
21,554
hi willhel,
As this Homework, please post what you think the right way to calculate the power, we can then help.
E
I moved your Thread to Homework.:)
BobTPH
Joined Jun 5, 2013
11,633
Power is not consumed, energy is consumed. Are you trying to calculate power or energy? Your misuse of your units indicates you do not understand the meaning of the two.
Edited to add: Power is energy produced ir consumed consumed per second. 1 Watt is one Joule per second.
MrSalts
Joined Apr 2, 2020
2,767
Power is measured in watts (typically) = volts x amps.
if power x time is the ENERGY required. A watt x one-second is a joule. However, for the electric company, watt x hours or 1000 Watt x hours or kWh
Im not sure where the hours come in from your data. If you are measuring them over a one hour period, then you need to integrate by adding each reading in your 1-minute time slice. The resulting sums of 1-minute average datapoints can be added to get kWh. Killowatt*Hours, not kilowatts/hour.