relay weld test detection
Priyanshu Pandey
Joined Aug 2, 2018
9
what is "neutral relay weld"
I had connected relays in line and neutral , and i want to check individually whether either of relay got stucked when i had given signal to open it?
I can detect for line but i am unable to detect for neutral relay whether it is got stucked or not?
jpanhalt
Joined Jan 18, 2008
11,087
Is the supply to the load AC or DC? How many sets of contacts does the relay have?
For DC, one simple solution is to put an LED and resistor across the relay contacts. When the contacts are open, the LED lights. If the contacts are welded closed or closed by the control voltage, the LED is out.
If you will post the circuit you are using, a more detailed answer can be given.
Priyanshu Pandey
Joined Aug 2, 2018
9
Supply is AC single phase 230V across Line and Neutral . the problem with detection of neutral as it willl always have zero volt either relay closed or open , so how can i detect neutral relay welded or stucked?
kubeek
Joined Sep 20, 2005
5,796
You can use a relay with force guided contacts, where the main contacts are mechanically linked to the detection contacts, so if the main contacts get welded the secondary contacts will not switch over when you energise the relay. But they are not cheap and generally not suited for high loads.
You could also add detection relays - one between the switched line and neutral, second one between switched neutral and line. One of these two will stay energized if one of the main contacts gets welded closed.
AlbertHall
Joined Jun 4, 2014
12,636
You could connect a mains voltage neon (neon + resistor) across each contact. When both cotacts are open both neons will light up. If both contacts are closed neithe neo will light up. If only one contact is open just one neon will be lit - the one across the open contact.
shortbus
Joined Sep 30, 2009
10,049
Wouldn't the bigger question be, why is the neutral going through a relay? Single phase industrial/motor control usually doesn't use a relay in the neutral.
AlbertHall
Joined Jun 4, 2014
12,636
If the purpose of using two relays is to reduce the problems caused if one conract welds, then both cotacts could be in series in the live lead.
Priyanshu Pandey
Joined Aug 2, 2018
9
It is connected to neutral relay as line and neutral can be interchanged and in that case problem should not persist.
I have problem associated with neutral relay as it have zero voltage on both side of relay contact whether contact is closed or open