Hi everyone,
I have a question about power resistor and I'd like to hear your opinion.
I have a pre-magnetize circuit for a power transformer (60kVA) and they use 2 resistors 15 Ohm 50W. The voltage here is 440Vac.
As far as I understand, the current flow those power resistors should not exceed 1.82 A. But if you apply 440Vac to them, the current is now 50A flowing to resistors. The process lasts 0.7 s and after that the contact K1 will be opened and the pre-magnetize is finished.
You can see the figure below. My question is that my calculations is correct and how to understand correctly the power resistors rated 15 Ohm/ 50W?

I have a question about power resistor and I'd like to hear your opinion.
I have a pre-magnetize circuit for a power transformer (60kVA) and they use 2 resistors 15 Ohm 50W. The voltage here is 440Vac.
As far as I understand, the current flow those power resistors should not exceed 1.82 A. But if you apply 440Vac to them, the current is now 50A flowing to resistors. The process lasts 0.7 s and after that the contact K1 will be opened and the pre-magnetize is finished.
You can see the figure below. My question is that my calculations is correct and how to understand correctly the power resistors rated 15 Ohm/ 50W?