In the Volume 2, Chapter 11 there is an example problem showing how to perform power correction:

http://www.allaboutcircuits.com/vol_2/chpt_11/4.html

My question is about the part where average power (the text calls it true power) is assumed to stay fixed when capacitive reactive power is added to inductive reactive power,

"This correction, of course, will not change the amount of true power consumed by the load, but it will result in a substantial reduction of apparent power, and of the total current drawn from the 240 Volt source."

How can we assume the correction will not change the amount of average or true power?
 

JDT

Joined Feb 12, 2009
657
Because the True Power is dissipated in the resistive part of the load. The inductive part does not dissipate power.

The capacitance that you add to improve the power factor also does not dissipate power. Therefore the true power remains unchanged.

(Provided the PFC capacitor is perfect, of course. Real capacitors will dissipate some power but this should be a very small proportion.)

The power factor correction reduces the supply current to a minimum (if the PF = 1). This reduces power dissipated in the wires and transformers conducting the current to the load. The power dissipated in the load remains unchanged.
 

Thread Starter

oogieoogieful

Joined Dec 2, 2013
6
When one adds capacitors in parallel, it changes both resistance and reactance of the impedance. Equivalent Impedance for components in parallel is

Z = ((1/R+jX)+(1/-jX))^-1

(This formula still treats the capacitor as if it were ideal, i.e. no resistance.)


If the capacitor were added in series, it would not change the resistive part of the
load, only the reactance part.

Z = (R+jX) + (-jX).

It appears that adding capacitors in parallel does dissipate power, the next question is how much?
 

WBahn

Joined Mar 31, 2012
33,122
In the Volume 2, Chapter 11 there is an example problem showing how to perform power correction:

http://www.allaboutcircuits.com/vol_2/chpt_11/4.html

My question is about the part where average power (the text calls it true power) is assumed to stay fixed when capacitive reactive power is added to inductive reactive power,

"This correction, of course, will not change the amount of true power consumed by the load, but it will result in a substantial reduction of apparent power, and of the total current drawn from the 240 Volt source."

How can we assume the correction will not change the amount of average or true power?
In the truly general case, you can't assume that adding a reactive component won't change the real power. But in this case you can. The reason is that the capacitor is added in parallel to the source and therefore has no effect on the voltage applied to the load which then means that the load sees nothing different at all -- is still draws the same current at the same phase angle. That current can be viewed as the superposition of two currents, one that goes to the resistive part of the load and one that goes to the reactive part. The only thing the capacitor does is make it so that the current that is going to the reactive part is shuttled back and forth between the load and the capacitor while the source provides the current that goes to the resistive part of the load.

If you were to include line resistance between the source and the capacitor, then you would see the addition of the capacitor result in a change in the real power dissipated in the load. The effect here is that, by reducing the current drawn from the source, there is less of a voltage drop in the line resistance and a corresponding increase in voltage appearing across the load.
 

Thread Starter

oogieoogieful

Joined Dec 2, 2013
6
If the load has any resistance (not equal to 0 ohms) the voltage across it will change when capacitors in parallel are added. (To be clear, the set-up I am describing does not take into account a line resistance.)

Given a load with an impedance Z = R + jX and capacitive impedance Z = -jX

The new impedance is Z = r +jX.

If R is Resistance before capacitor is added and r is resistance after capacitor is added in parallel, does R = r?

One must first find equivalent impedance of load and capacitor. For components in parallel:

Z = ((1/(R+jx)+(1/-jX))^-1 = ((R+jX)(-jX))/((R+jX)+(-jx)) = r +jX

The only way the R = r is if the R = 0.

Is the author claiming that R = 0 for the load in the diagram? I doubt it.

The assumption must be something like the difference between R and r does not change the voltage across the load enough to matter.
 

WBahn

Joined Mar 31, 2012
33,122
The problem is that you are answering a question about oranges by analyzing apples.

The claim is that the average power dissipated in the load is unchanged, not that the resistive component of the load impedance is unchanged.
 

Thread Starter

oogieoogieful

Joined Dec 2, 2013
6
My post responded to your claim, "The reason [one can assume that adding a reactive component wont change the true power] is that the capacitor is added in parallel to the source and therefore has no effect on the voltage applied to the load which then means that the load sees nothing different at all -- is still draws the same current at the same phase angle."

I am showing how the voltage across the load does change when capacitors are added in parallel, since the impedance changes. According to Ohm's Law, the load cant draw the same current at the same phase angle.

That is why I think analyzing the impedance is relevant.

I am not claiming it is changing voltage of the supply, but the load. Perhaps this is where my reasoning goes wrong?
 

WBahn

Joined Mar 31, 2012
33,122
If the voltage across the load changes, then that must mean that the voltage across the supply changes, right? After all, they are in parallel. But how can the voltage across an ideal voltage source change?

Give me an example of a simple circuit, configured like this one, in which the voltage across the load changes (and, no, you can't make the load impedance zero).
 

Thread Starter

oogieoogieful

Joined Dec 2, 2013
6
Okay, I do see how I was writing about the voltage supply wrong. But I think I am right that the load draws neither the same current nor a current at the same phase angle. Isn't that the whole point of power correction?
 

WBahn

Joined Mar 31, 2012
33,122
If I tell you that the voltage across a load with a particular impedance is Vbob, can you tell me the current, both magnitude and phase, through that load? If I then make some changes on my side of a wall and tell you that the voltage is now Vfred, can you tell me the new current? What will the new current be relative to the old current if Vfred and Vbob are the same?
 

Thread Starter

oogieoogieful

Joined Dec 2, 2013
6
Yes, I would apply Ohm's Law, since the voltages is constant, the current depends on the impedance.

If the impedance does not change, the new current is the same.

If the impedance does change, the new current will be different.

Furthermore, the change in impedance depends on how the circuit was changed, namely were component(s) removed/added in parallel or in series.
 
Last edited:

WBahn

Joined Mar 31, 2012
33,122
Yes, I would apply Ohm's Law, since the voltages is constant, the current depends on the impedance.

If the impedance does not change, the new current is the same.

If the impedance does change, the new current will be different.

Furthermore, the change in impedance depends on how the circuit was changed, namely were component(s) removed/added in parallel or in series.
But the impedance of the load did not change, hence the current in it does not change.

The component that was added was a capacitor added in parallel to the load.

The load sees NO change. The source DOES see a change. From the source's viewpoint, it sees a net load the has a different impedance than the original load. But the question wasn't about the current that the source delivers, it was about the average power dissipated by the load. If the load sees no change in the source source powering it, then the power dissipated in it doesn't change.

Do the math! Figure out the average power dissipated in a generic load having an impedance of Z=R+jX. Then put a capacitor in parallel with it and figure out the average power dissipated in that same load. Then compare them.
 