Messed up ground, solution?

Thread Starter

vladtess

Joined Jan 5, 2011
43
Hello fellas. I have a large building with multiple ground points, some are via copper rods, some are via pipes. However the ground is contaminated: one of the phases is connected to ground so ground (green) wire is always under power (unsafe?). The thing is that I cannot fix it, some rooms are locked so I won't be able to find the source of the problem. Now can I fix it by simply inserting two more rods into surrounding area (and measure resistance) and create a safe ground? Will that create a safe alternative? Thanks much!!!!
 

MaxHeadRoom

Joined Jul 18, 2013
30,654
However the ground is contaminated: one of the phases is connected to ground so ground (green) wire is always under power (unsafe?). The thing is that I cannot fix it, some rooms are locked so I won't be able to find the source of the problem. Now can I fix it by simply inserting two more rods into surrounding area (and measure resistance) and create a safe ground? Will that create a safe alternative? Thanks much!!!!
Need a bit more information? If one of the phases is connected to ground is this to form a neutral as in one corner of a delta system grounded or is it what is euphemistically known as a wild or high leg system to obtain a neutral?
In what way is one phase connected to earth ground a danger?
Max.
 

MaxHeadRoom

Joined Jul 18, 2013
30,654
However the ground is contaminated: one of the phases is connected to ground so ground (green) wire is always under power (unsafe?). The thing is that I cannot fix it, some rooms are locked so I won't be able to find the source of the problem.
Or is this a case of a phase being grounded that otherwise is above ground?
If so it would (should) trip a breaker or blow a fuse if it has a separate grounded neutral?

A definitive source is SOARES Book on Grounding published by the IAEI (Electrical Inspectors Assoc) Of which the NEC grounding definition is based on.


I doubt if it helps, but every one of my barns/shops; has an individual ground rod.
This is fairly normal, especially if they have their own service panel.
Max.
 
Last edited:

mcgyvr

Joined Oct 15, 2009
5,394
Without knowing your location one cannot give a proper/complete answer.
In the US you should reference article 250 of the National Electrical Code as well as any other applicable sections.
Also what is meant by the "ground is contaminated" ?

You also MUST find the building super or whoever can "unlock" these locked rooms.

Are you even a licensed electrician?
 

#12

Joined Nov 30, 2010
18,224
Agree!!! This might be a life or death situation. You absolutely must understand the whole circuit or get somebody that does. No guessing allowed!
 

inwo

Joined Nov 7, 2013
2,419
Hello fellas. I have a large building with multiple ground points, some are via copper rods, some are via pipes. However the ground is contaminated: one of the phases is connected to ground so ground (green) wire is always under power (unsafe?). The thing is that I cannot fix it, some rooms are locked so I won't be able to find the source of the problem. Now can I fix it by simply inserting two more rods into surrounding area (and measure resistance) and create a safe ground? Will that create a safe alternative? NO!!!Thanks much!!!!
...............................................................................................
 

inwo

Joined Nov 7, 2013
2,419
From my experience from working with those on other sites, there are still some UN-orthodox methods used out there, it is not the fault of the person having to operate with the system.
Max.
True.

Repairs to an unknown system by an inexperienced person is another story.
 

Thread Starter

vladtess

Joined Jan 5, 2011
43
We'll I'm not sure about configuration. Just thought that this May not be normal and looking for ways to fix it. I'm in New York.
 

mcgyvr

Joined Oct 15, 2009
5,394
oh boy..
Just stop now before you kill yourself or someone else.
If there is any need for electrical inspection/modification in that building you MUST call a licensed electrician.
This isn't a job for you..
 