Looking for reference designs for replacing MCBs/contactors with a solid-state protection & switching system (120V / 120A)

Thread Starter

rakesh1111

Joined Oct 1, 2026
1
Hi everyone,

I’m working on a system where I want to eliminate the conventional mechanical protection/switching components such as MCBs, DC contactors, and similar devices, and replace them with a fully electronic/solid-state solution.

The target electrical system is approximately:

- DC bus: 120 VDC

- Continuous current: up to 120 A

- Power: ~14.4 kW

- High inrush/capacitive loads may be present

- The system should be able to turn the load ON/OFF electronically

- Ideally it should provide bidirectional blocking when OFF

- Low conduction loss is important

My initial idea is a back-to-back N-channel MOSFET architecture, potentially using multiple MOSFETs in parallel to achieve the required current capability.

However, I don't want to simply make a MOSFET switch. The goal is to develop something that can potentially replace the functionality normally provided by MCBs + contactors + additional protection circuitry in one solid-state system.

I'm looking for advice on the overall architecture and, especially, real hardware/reference designs that have actually been built and tested.

Functions I'm trying to achieve

  1. 120 VDC / 120 A continuous switching
  2. ON/OFF control
  3. Bidirectional blocking in the OFF state
  4. Overcurrent protection
  5. Fast short-circuit protection
  6. Controlled turn-on / inrush-current limiting
  7. Precharge for capacitive loads
  8. Over-temperature protection
  9. MOSFET gate protection / UVLO
  10. Fault latching and safe shutdown
  11. Detection of a MOSFET that has failed short
  12. Current monitoring
  13. Bus/load voltage monitoring
  14. Possibly electronic trip characteristics similar to an MCB
  15. Ability to reset/reconnect electronically after a fault, where safe
  16. Controlled shutdown of the load
  17. Protection against inductive/transient energy
Architecture I'm considering

Something along the lines of:

120 VDC → fuse/current sensing → precharge branch + main B2B MOSFET bank → load

For the main switch, I'm considering multiple high-voltage N-MOSFETs in parallel on each side of the back-to-back arrangement.

For example:

4–8 MOSFETs per direction/blocking stage, depending on the selected MOSFET and thermal requirements.

The gate drive would probably need a floating/isolated supply and dedicated gate driver, with individual gate resistors, gate-source protection, and hardware fault shutdown.

For protection, I'm considering having a fast hardware overcurrent/short-circuit path independent of the MCU, with the MCU handling slower functions such as monitoring, diagnostics, thermal management, precharge sequencing, etc.

What I'm particularly interested in

I'd really appreciate references or practical experience with:

- Solid-state replacement for DC contactors

- Solid-state replacement for DC circuit breakers / MCBs

- 100–150 V / ~100–150 A MOSFET circuit breakers

- Back-to-back MOSFET arrangements

- Parallel MOSFET current sharing

- Fast hardware short-circuit protection

- MOSFET SOA during a hard short circuit

- High-side N-MOSFET gate driving at ~120 V

- Precharge circuits for large capacitive loads

- High-current DC current sensing

- Thermal design for 10–15 kW solid-state switches

- Fault latching and electronic trip systems

- Detecting MOSFET failure/short circuit

- Protection against inductive loads and DC transients

- PCB layout techniques for 120 V / 120 A

Reference designs I've found so far

I've come across some useful designs from TI and Infineon, such as:

- Infineon REF_60100EDPS eDisconnect

- TI 48-V / 50-A bidirectional circuit breaker reference design

- TI TIDA-010208

- TI TPS48110-Q1 EVM

- TI TIDA-020065 Smart Fuse

These are very useful, although most are below my final voltage/current requirements.

I'm particularly interested in actual schematics, evaluation boards, application notes, or products that have implemented this concept, even if they're only 48 V / 50 A or similar. I can scale the power stage if the underlying protection and control architecture is appropriate.

I’m not necessarily looking for a single IC that handles 120 V / 120 A. I'm open to a discrete architecture using MOSFETs, gate drivers, current sensors, comparators, MCU, etc.

The bigger question is:

What would be a robust architecture for replacing the combination of a DC MCB + contactor + protection circuitry with a solid-state system at ~120 V / 120 A?

If you've designed something similar, I'd really appreciate any reference designs, schematics, application notes, papers, products, or lessons learned.

Also interested in hearing about approaches other than MOSFETs if there is a better solid-state technology for this voltage/current range.

Thanks!
 

Ian0

Joined Aug 7, 2020
13,312
The problem is that you system does not fail safe. Its most common failure would be a MOSFET going short circuit, in which case the load is permanently energised and you cannot switch it off.
For 120V DC, nothing beats a fuse, and make sure that the fuse is rated to break the prospective fault current at DC. Many DC-rated MCBs are only rated at 80V.
 

MisterBill2

Joined Jan 23, 2018
28,550
The goals stated in post #1 are impressive indeed.
The responses in posts #2 and #3 are correct and reasonable.
CERTAINLY safety matters and IAN is totally correct about the suitability and reliability of a good fuse.
As for the attaining of the stated goals, consider that multitudes of brilliant engineers and designers have sought most of them for at least 100 years.
The reality is that we must choose to work within the limitations of reality to do anything worthwhile. The stated requirements do not seem to be even reasonably achieveble in any practical situation.

I recall one of the salesmen, at a previous employer, who came up with a simple product specification: "The product shall not fail at any time under any condition".
 
Last edited:

MaxHeadRoom

Joined Jul 18, 2013
30,881
Is this intended for Niche, i.e. Dedicated circuits?
For the typical run-of-the-mill contactors for control circuits, there has been a Safety Relay avaiable, it has been prevelent in Europe for some time, but it seems slow catching on in N.A.
 

MisterBill2

Joined Jan 23, 2018
28,550
In my area of electrical work, an MCB is the "MAIN Circuit Breaker." IT has no other accepted meaning!!!
Consider that referencing a device by its size is rather ambiguous at best.

I Make a serious suggestion to all of the folks who want to communicate accurately to avoid using such abreviations as have different meanings in different parts of the world. REALLY!! Using a term that has so little actual information does not benefit others.
 

MaxHeadRoom

Joined Jul 18, 2013
30,881
For electrical control enclosures in NA, the NFPA79 covers these.
So NFPA 79: Electrical Standard for Industrial Machinery indicates that thier term MCB = Miniature Cicuit Breaker..
 

MisterBill2

Joined Jan 23, 2018
28,550
For electrical control enclosures in NA, the NFPA79 covers these.
So NFPA 79: Electrical Standard for Industrial Machinery indicates that thier term MCB = Miniature Cicuit Breaker..
I never implied that the term was not correct!!
BUT the fact is that not everybody who visits this site is familiar with every trade-specific abreviation. THAT includes ALL of them. Just because an abbreviation is officially recognized does not mean it is known by everybody!!
COURTESY SUGGESTS taking a bit of effort towards clarity!!
 

MisterBill2

Joined Jan 23, 2018
28,550
the MAIN Circuit Breaker protects the supply circuit from an overload from the breanches. The individual BRANCH breakers in some of the the breaker panels I have seen are similar sized to the main breakers. BUT in many other panel the branch breakers ARE SMALLER than the main breakers.
ALWAYS, referencing items by size is leaving room for confusion. BRANCH Breaker leaves no room for confusion.
IN several brands of breaker panels the sizes are different, in others the main breaker is physically the same size, BUT rated for either 60amps or 100 amps.

As for a fully solid-state (semiconductor) replacement for an actual breaker or fuse, I would not trust them to provide a total shutoff of power. AND!! TOTAL shutoff is the alternative to working o a HOT circuit.
 
Last edited:

MaxHeadRoom

Joined Jul 18, 2013
30,881
IMO, solid state safety breakers would inherently be rather unsafe, this is probabally why they are seldom/never seen for circuit protection purposes!?
What is the reason for the need?
It is customary to manually reset a safety breaker, rather than have it automatic reset.
 

MisterBill2

Joined Jan 23, 2018
28,550
I Totally Agree with MAX , in post #11!! There are certainly many applications for solid state technology, but positive circuit breaking is not one of them!! "AIRGAPs between contacts" have a good record of not failing.
 

ZhangSheng

Joined Sep 25, 2026
17
At this power level I would keep the solid-state switch and the safety disconnect as two different jobs, even if the final product looks like one box. A MOSFET bank is excellent for controlled switching, precharge and fast current limiting, but a failed-short device cannot open the circuit, so a series fuse or other proven disconnect that is rated to interrupt the prospective fault current is still needed for service isolation and for a hard short.

For the switch itself, the most important split is between the fast hardware trip and the controller. Use a hardware current-sense comparator and latch for the short-circuit path, independent of firmware, with a slower firmware loop only for overload curves, temperature derating and retry policy. That way a controller lock-up cannot delay the first trip.

For paralleling, give each device its own gate resistor and a symmetric, low-inductance layout, and check sharing under both steady load and a short pulse, not only at room temperature. Small differences in gate threshold and board resistance show up quickly at 120 A. Size the copper, busbars and heatsink for continuous conduction loss plus the worst-case precharge energy, and verify the junction temperature with the enclosure closed, since the thermal path is usually the limit before the silicon rating is reached.

Precharge also deserves its own branch with its own current limit and timeout, so a failed precharge resistor or a shorted load capacitor is detected before the main bank closes. Finally, make fault latching the default after a short-circuit trip, with manual or deliberately confirmed reset, rather than automatic reconnection into an unknown load.
 

panic mode

Joined Oct 10, 2011
5,448
conventional eFuse ICs go up to 80V and are limited by internal mosfet to some 20A max.
what you need is hot-swap controller architecture - with external mosfets. they too often go to 80V but if floated, this is not a problem. external mosfets can handle the load. this must be accompanied by freewheeling diodes and TVS arrays since stopping high current in short time creates massive surge.
 
Last edited:
CERTAINLY there are, and have been, solid state power switch packages that include all of the requested protective functions described. Unfortunately, it seems that those packages cost more than the traditional systems of similar ratings.
 