I have two linear actuators and a control module. The actuators have 2 pole reversable power leads and a 3 wire hall sensor assembly on the back of the motor.
Either the control module is the problem or the hall sensor on one of the actuators is the problem. Unfortunately, Im not sure how to test these sensors to narrow it down.
Honestly, I was hoping for leaf switches. I have very little grasp of electronics beyond building a timing circuit here and there. Im at a loss as to how the hall sensor is providing positional information and my best guess is that is just indicating stop and go.
Would anyone be kind enough to enlighten me on this? I can provide photos if needed.