hi can you assist me with TDC i am wiring a control box for 100ton press i am using contactors relay and a limit switch or a pnp sensor.
i wired the contactor to the sensor but the sensor cuts the conactor and i can start again
all i want is to cycle the press and stop on tdc and be able to reset and start again
shortbus
Joined Sep 30, 2009
10,049
Not so sure you can do it with your sensor. A limit switch yes, because they have two different contacts in them, a NO and a NC. The NC would get opened when the crank or ram hits TDC shutting off that contactor/relay. And the NO would close at TDC enabling the start contactor/relay to work for the next cycle.
strantor
Joined Oct 3, 2010
6,875
Wire your sensor to a relay, use the relay contacts to break power to the contactor coil. The relay can be configured in a latching way so that you press and release the button and the press runs until the sensor is activated (auto mode) and then to keep going or to retract, you can hold the button in (manual mode).