Is this what you are describing?Good day all,
Any one with idea on how to achieve this Changeover I would like to make.
I want to manually switch my Refrigerator to Inverter AC power using a simple Switch + 12v DPDT Relay on NO. But when Grid power is restored, the Relay should automatically be switched back to Grid on NC so the Refrigerator continues on Grid power but when the Grid goes off, theRefrigerator goes off. So to use the Refrigerator on Inverter, I need to use the switch again.
I hope the explanation does it.
Thanks

Operation:
1.0 Grid Power on:
--------------------
1.1 K3 energized. K1,K2 de-energized.
1.2 GRID supplies House power
2.0 Grid Power Loss:
--------------------
2.1 K3 de-energizes
2.2 House power loss
3.0 Manual power transfer
--------------------
3.1 XFR Pushbutton is pressed and released.
3.2 K1 energizes and latches via K3 NC contact.
3.3 K2 energizes via K1 NO contact and transfers house power to inverter.
3.4 House power re-established.
4.0 GRID power returns:
--------------------
4.1 K3 energizes. K3 NC contact unlatches (de-energizes) K1.
4.2 K1 NO contact de-energizes K2
4.2 House power returns to GRID power.
5.0 repeat from 1.0