Thank you so much for the response! Everything you've stated makes sense and I 100% agree with you. What I didn't know is the large transient load on the power feed; I didn't even think of that.In most industrial applications, where there are multiple motors that each have a starter, such as is described in this post, things are a bit different.
First, each motor has a a separate start button, because starting all of the motors at once puts a very large transient load on the power feed. Usually each motor has it's own stop button, but not always.
The emergency stop will switch off all of the motors, and none of them will start when the E-Stop is reset. So if the system is set up that way, then the set of contacts on the E-Stop button that close when it is pressed can sound the audible alarm, because resetting the E-Stop button does not start anything. That arrangement is often used for industrial systems, where a machine could harm an operator if it started at the wrong time.
If those "relays" are actual motor starters then they should have another contact for holding the coil powered when a start button is pressed.
So the big expense of this change will be getting four normally open, momentary action, start buttons.
And the maintained position E-stop button will need to have a set of contacts that close when it is pressed, in addition to those that open when it is in the "stop" position.
In this scenario, having multiple stop buttons is simply not an option but it's a good idea. Not all pump motors run all the time and not all at the same time.
The EPO button is maintained push / pull---closed when pulled; open when pushed--- EPO Maintained Push / Pull. What if I added something like a contact block onto the EPO button and utilize the NO contacts, would that give the ability for the 120V to operate the audible alarm?
The exterior mounted 2 gang box cover would look something like this...

The relays I'm using are below. I did not check if those relay were actually motor starters.

Should I be using something different other than the power relays above?
-Jake