double check my amps calculations
ozzylr
Joined May 7, 2015
1
I am installing a tank heater which stated a 10000 watt heater. It has a 220 plug so ifPower equals E x I then I equals W/E or in this case 10000/220. Am I right.? Does the fact that the 220 is made up of 110 on each leg affect the formula or the overall current?
12,272
No. 10 kW / 220 = 45.5 A. I'd say to use a 50 A breaker. but more experienced hands around here might recommend 60 A.
Reloadron
Joined Jan 15, 2015
7,946
Here in the US for a 10 KW heater load I would run a 240 VAC 60 Amp service disconnect fusible type (2 fuse) 3 wire using AWG 6 3 conductor. Your current will be as Analog stated 10 KW / 240 V = 42 Amps or if the mains voltage for your location is 22 then about 46 Amps. Just make sure for your local you use a correct wire gauge for the load and meet any other building or code requirements.
Ron