Delta VFD stopped stopping

Thread Starter

benha

Joined Jan 4, 2011
76
Howdy.

I have an older Delta VFD (VFD075A23H) that just started giving me issues. It's connected to the spindle on a CNC router. For the entire time I've had it, it's been happily working, driven from a PC running Mach3, connected via a PMDX-107 speed control board connected to a PMDX BOB. I fiddled with some settings this morning because I realized that I could reduce the minimum spindle speed by futzing with the control frequency. After this, the VFD stopped turning the spindle off as it's supposed to.

As part of my debugging effort I've now removed the router control wiring and am controlling it just with the VFD's onboard panel. Even like this it won't shut off.

I can start the spindle and increase the frequency just fine.
I hit the stop button and the Run light starts flashing and the Stop light illuminates.
But the spindle keeps spinning.

I've tried resetting the spindle to factory parameters which I think worked to reset the values - it's a bit hard to tell - but it didn't change the result. Still won't turn off.

I'm starting to think that something got fried inside the VFD when I changed the operating frequency, but that just seems odd.

Anyone have suggestions for how to get this thing working again?

-Ben
 

lichurbagan

Joined Jul 4, 2025
120
Check keypad switch continuity (with power off) to rule out a failed STOP switch on the panel.
Power off, open the panel, measure continuity of the STOP button while pressing it. If the STOP switch contact is open or not changing, replace/fix the panel switch membrane.
 

Thread Starter

benha

Joined Jan 4, 2011
76
Yeah, the button clearly works because when pressed the STOP LED comes on and the RUN LED starts blinking. It just doesn't change the behavior of the spindle. Argh.
 

JohnSan

Joined Sep 15, 2018
121
So.
What settings did you fiddle with?
Were they in the VFD or some other component?
I don't think setting to default values did you any favours.
 

Thread Starter

benha

Joined Jan 4, 2011
76
Fixed! Turns out the default value for Over-voltage Stall Prevention was "on" and that was causing the thing to just keep running for some reason. Disabling that allows it to ramp to a stop. Yah!
 

Thread Starter

benha

Joined Jan 4, 2011
76
Heh. Would be a lot nicer drive if it would actually ALERT you to the overvoltage trigger, rather than just silently not stopping :)
 

panic mode

Joined Oct 10, 2011
4,864
overvoltage sensing sounds like a rather vital feature. what makes you think that turning this off is 'fixing' the problem and not merely masking it?

btw. most drives i have worked with have built in braking resistor of low power (only some have none), and option to add external braking resistor of high power. braking resistors are used to absorb excess energy from spinning motor while decelerating. failure to do that is risking blowing up the IGBTs. that is why warning is there - to make you aware of the issue so you can do a proper fix instead of continued blows to the IGBTs. you need to choose reasonable decel time or use external braking resistor of high power (and lower internal resistance).
 
Last edited:

Thread Starter

benha

Joined Jan 4, 2011
76
overvoltage sensing sounds like a rather vital feature. what makes you think that turning this off is 'fixing' the problem and not merely masking it?

btw. most drives i have worked with have built in braking resistor of low power (only some have none), and option to add external braking resistor of high power. braking resistors are used to absorb excess energy from spinning motor while decelerating. failure to do that is risking blowing up the IGBTs. that is why warning is there - to make you aware of the issue so you can do a proper fix instead of continued blows to the IGBTs. you need to choose reasonable decel time or use external braking resistor of high power (and lower internal resistance).
From what I've read since I started chasing this, this internal overvolt protection parameter is not reactive, it's proactive. It looks at the deceleration time you set, and then ASSUMES that you're connected to a high-inertia load like a fan or conveyor or something, and if the deceleration time is too short for that use case it trips the protection. But I'm not driving a high inertia load. I'm driving a CNC spindle. It has very low inertia. So none of the internal assumptions about the load are correct, meaning it's being over protective.

I take this with a grain of salt since my understanding is informed in part by ChatGPT's often-flawed analysis. But in this case it's making sense.

There are other, reactive protections that are still in place to protect the drive.
 

panic mode

Joined Oct 10, 2011
4,864
also look at the linked video about 4:26. you will see staircase graph, going down. the steeper slope is what you desire but during this 250ms or so there is no correction - this is running purely on time.

in 250ms voltage can shoot WAY above limits of the drive. imagine wave traveling and then slamming at the wall. you will see upon impact that water is shooting upwards (just like voltage). the more energy the wave has, the higher the water reach.

then think about failure modes... material destruction due to high voltage is extremely fast. even if it device still appears to function, it IS scared... think Lichtenberg figure. then thing what happens over time. how many such events will take till total destruction?

i work with robots so normal D bus is 600 - 650VDC, IGBTs tend to handle 750-800V, though some may be 1200V models. without braking resistors, they do get destroyed. not every time but plenty of the time.

in comparison to overvoltage damage (nano to micro seconds), overcurrent damage is much slower... several ms to several seconds (or slower), because temperature is a much slower process than pressure (or voltage). so 250ms or so shown in video is an eternity... may as well be 2 hours.
 