What is the circuit diagram to connect a single phase load to a 3-phase synchronous generator (PMG) having 3 output wires
True.For truly balanced loads however, it would require three loads across each pair.
Max.
Thanks,For truly balanced loads however, it would require three loads across each pair.
Max.
Thanks very much for your reply.Here's a diagram if you really need it.
View attachment 171408
You cannot connect a single phase load to a 3-phase 3 wire generator. Stop.What is the circuit diagram to connect a single phase load to a 3-phase synchronous generator (PMG) having 3 output wires
What is the RMS Voltage between any two Phase Wires of your generator?What is the circuit diagram to connect a single phase load to a 3-phase synchronous generator (PMG) having 3 output wires
I read more than what was written by the OP.So what if he has 400v loads, it will work perfectly well.!!?
Or whatever the phase to phase voltage is.
A phase to a phase IS single phase.
Max.
Not true. Line voltage is phase voltage in a Delta. We run lots of single phase loads off of Delta.√
You cannot connect a single phase load to a 3-phase 3 wire generator. Stop.
3 phase output with 3 wires is obviously a Delta connection. The voltage will be √3 times the Single Phase voltage.
This means the if Single phase is 230 Volts, the Phase to Phase voltage will be 400 !!!
If you connect a Single Phase Load across any 2 wires of the generator, it's goodbye to the Load, Generator or both with, maybe, a lot of sparks and smoke as an added show.
You will need to use a Delta - Star Transformer to derive the 3 Phases with Neutral so that you can connect your Single Phase load.
We have no idea what the OP's generator output is.I read more than what was written by the OP.
A single phase load is normally 110 / 220 Volts. Not 190 or 400.