Can I Stack Busbar with Different Thickness ?, Stack 3mm x 20mm with 5mm x 20mm
Thread Starter meowsoft Joined Feb 27, 2021 607 Feb 27, 2021 #1 Can I Stack Busbar with Different Thickness ?, Stack 3mm x 20mm with 5mm x 20mm
MaxHeadRoom Joined Jul 18, 2013 28,060 Feb 27, 2021 #2 I don't see why not? Power distribution panel? AS long as correct insulation/isolation from frame is observed. Max.
I don't see why not? Power distribution panel? AS long as correct insulation/isolation from frame is observed. Max.
Deleted member 115935 Joined Dec 31, 1969 0 Feb 27, 2021 #3 just be careful about temperature rise, especially if the bars are insulated,
Thread Starter meowsoft Joined Feb 27, 2021 607 Mar 1, 2021 #4 Ok... that bar is not insulated, how many amps can 20mm x 3mm copper busbar handle ? How to calculate ?, 230v/400v AC
Ok... that bar is not insulated, how many amps can 20mm x 3mm copper busbar handle ? How to calculate ?, 230v/400v AC
MaxHeadRoom Joined Jul 18, 2013 28,060 Mar 1, 2021 #5 Approximately 250a - 300 amps in free air. https://www.australwright.com.au/technical-data/advice/copper-busbar-rating/ Max. Last edited: Mar 1, 2021
Approximately 250a - 300 amps in free air. https://www.australwright.com.au/technical-data/advice/copper-busbar-rating/ Max.
Thread Starter meowsoft Joined Feb 27, 2021 607 Mar 1, 2021 #7 MaxHeadRoom said: Approximately 250a - 300 amps in free air. https://www.australwright.com.au/technical-data/advice/copper-busbar-rating/ Max. Click to expand... What's About Busbar Derating ?
MaxHeadRoom said: Approximately 250a - 300 amps in free air. https://www.australwright.com.au/technical-data/advice/copper-busbar-rating/ Max. Click to expand... What's About Busbar Derating ?