Battery Charger Amp Draw from Wall

Thread Starter

Andy Larson

Joined Mar 26, 2015
51
I'm making a battery cart for my FRC team. We want to use multiple Noco G3500 Smart Charger, since a bank charger would need to be replaced if one channel fails, which is far more expensive. I'm running into a problem, I can't figure the ampere requirement from the wall. The datasheet meantions "Max Power" of 60, which means the amp draw is 500mA. But the charger is a 3.5A charger. Which do I use? I don't want to trip a breaker
 

MrChips

Joined Oct 2, 2009
30,813
Why would the Noco trip a breaker?
The max power drawn is 60W. That is equivalent to a 60W lightbulb.
The max current @ 120VAC is 60W/120V = 0.5A
 

Thread Starter

Andy Larson

Joined Mar 26, 2015
51
Why would the Noco trip a breaker?
The max power drawn is 60W. That is equivalent to a 60W lightbulb.
The max current @ 120VAC is 60W/120V = 0.5A
That was my only question, thank you. I wasn't sure wether it would hold amps throught. Don't explain please
 