Two comments:what I understand, the snubber isn't really needed for a purely resistive load, but it would be a good thing to have anyway (it can't do any harm and may prevent some false firing).
1. High values of dV/dt will turn on a triac. A snubber prevents this.
2. Triacs require a require a minimum load. Providing one means an open load means you measure 120V where the load would be even when off.
3. If your doing phase angle firing particularly, you have load options to consider.
1. Resistive heating - make P (0-100%) relate to V^2
2. Tunsten - e.g. UV heating
3. Inductive - Thing turns off at V=0 and I=0; Current limit is required
P is typically the variable for the output of a PID controller. It can vary -100 to 100% for heating/cooling application.
So, for resistive heating, you have to relate phase angle to 0 to 100%, to average voltage, squared. Since R is resistive and a constant, the 0-100% is linear related to power.