The described difficulty may owe to any of several conditions - prominent among them being:What could cause a drastic variation in voltage on a municipal supply to a house?
Assuming proper load-center OCP installation and absence of conspicuous arcing at or inbound of said load center - No!Is it possible that something on the house circuit side of thee main switch is causing it?
Tnx!Addendum:
Re: 120V--N--120V service - an open neutral may produce the described symptoms Re: the 120V circuits --- Said circuits being thence 'stacked' in a 'series-parallel' arrangement line to line - permitting an EMF range at any 120V receptacle of (essentially) 0V-240V (dependent upon load distribution)...
Best regards
HP
A good start would be to check the integrity of your neutral connection via observation of the 'cross-line' EMF (i.e. any 240V circuit) during an 'event' -- Stability of the 240V supply under said conditions implicates the neutral connection -- Be warned that a 'bad' neutral may damage 120V loads via an 'over-voltage' condition!Its an intermittent problem so I will have to wait for it to happen again and maybe make a video of my testing procedure and readings
Hi!define "drastic"?
State where/how you are determining there is a problem? Where are you measuring? What tool are you using?
If you are measuring at an outlet in the room then the problem could be anywhere upstream.. And up to an including the distribution box is your issue.. Before that would be the utilities problem and sometimes they will throw a logger on and check it over a period of time..
Voltage readings at this point of entry ranged between 0volts and 102 V (it is supposed to be, and is at the moment 230VHi!
Did all measurements at the point of supply entry on the main switch in the db box with a fluke T150 voltage tester
In usa ground and neutral aren't same thing cuz neutral is just center tap from transformer which is tied to ground and house wiring both so you still have neutral if you lose groundGround rods that connect to neutral at your breaker box do NOT last forever.
It is a bare copper to copper connection between rod and wire using only a compression collar.
Drive a new rod and make a new connection on clean copper.
Also know that very dry ground, such as you would experience during drought can cause a high resistance neutral conductor condition, and cause voltage fluctuations based on current draw.
If you checked it before main house breakers its utilities trouble and you should call right now cuz is probably arcing which is major fire hazard!Voltage readings at this point of entry ranged between 0volts and 102 V (it is supposed to be, and is at the moment 230V
Voltage readings at this point of entry ranged between 0volts and 102 V (it is supposed to be, and is at the moment 230V
If you checked it before main house breakers its utilities trouble and you should call right now cuz is probably arcing which is major fire hazard!
FWIW I wish to add my voice to those of @Aleph(0) and @mcgyvr --- Don't await recurrence of the malfunction! - Please report your observations ASAP! Additionally, please be advised that transformer explosion is possible in the event of internal arcing! ('Praise' be to supplanting chlorinated dielectric compounds with combustible hydrocarbon substitutesyep.. call them immediately.. If your readings are correct then its already arcing and a fire/total loss of electricity is soon to follow..
But its their problem not yours
Thanks for al the input and advice, I really appreciate it.FWIW I wish to add my voice to those of @Aleph(0) and @mcgyvr --- Don't await recurrence of the malfunction! - Please report your observations ASAP! Additionally, please be advised that transformer explosion is possible in the event of internal arcing! ('Praise' be to supplanting chlorinated dielectric compounds with combustible hydrocarbon substitutes)
Please take care!
Best regards
HP