4 pole RCDs controlling query
jane_electrics
Joined Feb 4, 2023
6
My first time here and I'm not sure if this is the right forum to post this thread. I have a couple of 4 pole RCDs controlling at least 5 miniature circuit breakers each with a common input for them all. I had the neutral to all the RCD output tied to the bar and when i push the test button they don't trip individually. Is it safe to remove all the RCD neutral output and take the neutral from the supply to the load directly ? With the neutral input still available
WBahn
Joined Mar 31, 2012
32,935
Try to come up with a thread title that summarizes the problem you are having or what you are trying find out. If you post in the wrong forum, we will move it to the correct forum so that it will attract the attention of members having particular interests better suited to your issue.
MaxHeadRoom
Joined Jul 18, 2013
30,695
The RCD should normally be effective without the neutral present, as the live conductors would still be referenced WRT earth GND.
You would have to test it to ensure the RCD supports it.
WBahn
Joined Mar 31, 2012
32,935
This is out of my wheelhouse, so I don't recognize what the term RCD is referring to. At first I thought it might be some kind of motor drive, but from the context, it appears to be some kind of fault protection device similar to a GFCI?
MaxHeadRoom
Joined Jul 18, 2013
30,695
RCD = Residual Current Device, = GFCI , term used more often in UK etc.
jane_electrics
Joined Feb 4, 2023
6
A Residual Current Device (RCD)is a sensitive safety device that switches off the electricity within 10 to 50 milliseconds if there is an electrical fault. An RCD is is designed to protect against the risks of electrocution and fire caused by earth faults. Wish i could get an answer to that. I live in Dartford London
WBahn
Joined Mar 31, 2012
32,935
Thanks, both of you. Now I can follow the discussion better. Max is definitely someone to listen to for these kinds of questions, and that's doubly the case for questions specific to U.K. codes and usage.
jane_electrics
Joined Feb 4, 2023
6
RCD's do not have ground/earth input. It's just 3 phase and neutral and it definitely won't function properly without a neutral input
MaxHeadRoom
Joined Jul 18, 2013
30,695
Yes you are correct, the neutral is used to power the internal electronics, usually I assume the supply is 3ph star connected source supply, with the star point grounded, ?
Ian0
Joined Aug 7, 2020
13,158
The neutral must go through the RCD. Otherwise it cannot detect "residual" current, which is the difference between the live and the neutral i.e. any current that has gone astray - presumably to earth and hopefully not via a person.
On a well balanced 3-phase supply there will be no neutral current, so the sum of the live currents will equal zero.
On a not-so-well-balanced 3-phase supply, neutral current will be present. If this does not go through the RCD it will trip.
jane_electrics
Joined Feb 4, 2023
6
Yes, the neutral must go through the RCD .is it necessary to take the neutral from the output of the RCD to the load ? I did combine all the neutral (6 RCD) to the output line and when i push the test button multiple RCD trips. So i ignored the output neutral of all the RCD since the neutral input is available for the protection circuitry to function
Ian0
Joined Aug 7, 2020
13,158
A Δ-connected load would need no connection to the RCD output terminal. If there were a fault in which current flowed to earth, it would still trip the RCD as the net current (vector sum of the three live currents) would no longer be zero.
If the load is balanced and star-connected, the theoretically, no neutral connection would be required as there is no neutral current, but I think it would be bad practice to ignore it.
if the load is three separate single phase loads, I.e. unbalanced, then the RCD would trip immediately if the neutral were not connected via the RCD.
The trip button operates by connecting live at the output to neutral at the input through a resistor, allowing a current of ΔI (the tripping current) to bypass the current balance transformer thus simulating a fault current, so the trip button would not work without a neutral connection.