2 Phase Input to Single Phase SMPS

Ian0

Joined Aug 7, 2020
13,126
No. If you connect it between two of the three phases of a supply that is 230V AC phase-to-neutral, you get 400V. It won't like that.
 

LesJones

Joined Jan 8, 2017
4,511
If you are working on anything electrical you need some type of multimeter. If you are working on three phase supplies you need to understand three phase supplies. If you are in north America some people call the two live and neutral sytem 2 phase. It is realy single phase with the center tap of the distribution transformer connected to ground. this is the neutral wire. So you would measure 230 volts between the two live wires and you would measure 115 volts between neutral and either live wire. This means that if you are nominally at ground potential you would only get a 115 volt shock. With the european system live is about 230 volts with respect to ground so you would get a 230 volt shock.
Les.
 

MisterBill2

Joined Jan 23, 2018
27,469
Certainly a direct connection across 600 volts, or even 300 volts, is quite likely to cause immediate damage and destruction of that supply module.
How is the supply voltage for this device provided in the actual application??
An actual isolation transformer with a 4 to one step-down ratio would allow testing within the allowed voltage limits. That could be a quite small transformer as there is no need to provide the specified inrush starting current. , but only the operating current.
 