I like when I try to do things the wrong way and there are unintended benefits.If the extraneous windings are not conducting current then they are not generating heat. You may not have to de-rate it at all.
That all makes perfect sense. I trust you say this from experience; sounds like something you would try.When running a three phase transformer as a single phase unit you can use the two outermost winding sets in parallel which will give you near full rated capacity. If you run all three primaries in parallel the center winding set needs to be wired out of phase with the the other two but most transformers will go into core saturation if you do it thus the recommendation to just run with the outer two sets instead.
Secondaries of all three can be configured however you want though.