+/-15 VDC Power Supply

Thread Starter

JCapron

Joined Jul 4, 2016
11
I am looking for a circuit diagram for a dual output, +15/-15 VDC, 1.0 amp power supply. The power supply has to be low voltage input, either 24 VAC or 24 VDC. I am trying to replace the 120 VAC power supply that we have used in the past. I can find lots of examples of 120/240 VAC power supplies that all use center tap step down transformers. However, I cannot find a 1:1 CT 24 VAC transformer to adapt those circuits to a Class 2 application.

I also cannot find a circuit that uses a low voltage DC input that produces a dual +/-15 VDC output. Thanks for any advice.
 

AlbertHall

Joined Jun 4, 2014
12,347
However, I cannot find a 1:1 CT 24 VAC transformer to adapt those circuits to a Class 2 application.
Do you need to isolate the outputs from the input if you are using 24VAC input?
If not then you can use this circuit to get ±33V and then use 7815/7915 to get the regulated outputs. Mote that the 33V is very close to the maximum input voltage allowed (35V) so how accurate is the 24VAC?
upload_2018-5-20_1-5-33.png
 

ebp

Joined Feb 8, 2018
2,332
I think it will be nearly impossible to find an off-the-shelf transformer that is suitable.

I would suggest you look for a DC-DC converter. The drawback to a switcher is that the output noise will generally be higher than with a linear supply, which may be a consideration. External filtering can be added.

Something from the TDK/Lambda PXE30 series would do the job. They are not cheap, but quality should be excellent.
 

Thread Starter

JCapron

Joined Jul 4, 2016
11
With respect to AlbertHall, post: 1271028, member: 240904, "[Note] that the 33V is very close to the maximum input voltage allowed (35V) so how accurate is the 24VAC?"

The Class 2 transformers are not very accurate. I have seen the half wave peak as high as 39V under normal operation. These systems are installed in commercial buildings with backup generators, and the generator power is pretty sloppy.

With respect to crutschow, post: 1271032, member: 19451, "Where is the 24VAC coming from? Can you explain why you want to use that voltage instead of the 120VAC line voltage?"

Quite a bit of the building controls are powered by low voltage, power limited (24VAC) NEC Class 2 sources. This is a very common practice in heating and cooling systems in residential, commercial and institutional buildings. Class 2 eliminates the need for a lot of the installation standards that come with 120VAC, 240VAC or 277VAC that power receptacles, lights, etc. We use a lot of 24VAC to xxVDC power supplies for controllers, sensor, cameras, etc. In this case, we need +15/-15 VDC power supplies.
 

be80be

Joined Jul 5, 2008
2,072
So there's no problem with drawing a couple amps from that 24VAC source?
There good to about 1.5 amps the fuse blows at 3 amps but most times it about burns the transformer out too if you blow the fuse to many times.

But most are rated for 3 amps but then I do fix a lot that burn out and have a 3 amp fuse
I try to keep it around 1.5 if it me.

What happens is you add stuff to the sys they was made to run maybe 4 relays and a handful of senors 2 control boards most come in at 1 to 1.5 amps I wouldn't add something that pulls a amp on top of the load it takes care of.
 
Last edited:

Thread Starter

JCapron

Joined Jul 4, 2016
11
NEC Class 2 is deemed to be 100VA for circuits that operate at 30V or less. The circuits are fused or otherwise protected. Two (or three) amps would not be an issue. We routinely install 75 VA transformers.
 

be80be

Joined Jul 5, 2008
2,072
A 75VA transformer can't output but 2 amps then you have load's from what it was being used for.
Here the power company add a power saver board to the HVAC sys you see burnt out 75VA transformers all the time.
LOL

Guess you reading this lol
Only the load side of a power supply with a nameplate rating of less than 100VA (or 5 times Vout if output voltage is lower than 20V) can meet the class 2 circuit requirements.
 

be80be

Joined Jul 5, 2008
2,072
A 100 VA transformer max output is 2.6 amp @24 volts regulated DC now figure your total load to not use more then that but I would add headroom.
I wouldn't go over 2 amps
 

AnalogKid

Joined Aug 1, 2013
11,056
Without knowing what the +/-15 V is used for, it is impossible to say for sure; but my *guess* is that a non-isolated converter circuit such as post #2 will cause problems.

ak
 

Thread Starter

JCapron

Joined Jul 4, 2016
11
A 100 VA transformer max output is 2.6 amp @24 volts regulated DC now figure your total load to not use more then that but I would add headroom.
I wouldn't go over 2 amps
A 100 VA Class 2 transformer amperage is slightly over 4 amps (AC).
 

Thread Starter

JCapron

Joined Jul 4, 2016
11
Without knowing what the +/-15 V is used for, it is impossible to say for sure; but my *guess* is that a non-isolated converter circuit such as post #2 will cause problems.

ak
I agree. The 120 VAC +/-15VDC power supply we use now is isolated. A new 24 VAC power supply output would be +15 VDC and -15 VDC with shared common, ±5%, isolated, 1000 mA, 50 mV P-P maximum ripple. The only hurdle I have is the 24 VAC input.
 

AnalogKid

Joined Aug 1, 2013
11,056
The only way to get the flexibility of the fully isolated outputs in the original supply is to have fully isolated outputs in the replacement supply. To the original question - yes, there is an off-the-shelf transformer you can use. A small 1:1 isolation transformer will run just fine at 24 Vac instead of 115 Vac:

http://catalog.triadmagnetics.com/Asset/N-68X.pdf

Drive the secondary with 24 Vac, and you get two *isolated* 24 Vac outputs you can go crazy with. $16 at Digi-Key. Since the outputs are isolated from each other, you can use identical LM317 regulators for both the + and - outputs. Better regulation than the 78xx series, plus a higher input-voltage tolerance. ebay modules are $2.

If you don't like that part, DK (Newark, Allied, whatever) has many active, in-stock alternatives to choose from:

https://www.digikey.com/products/en...ty=0&ColumnSort=0&page=1&stock=1&pageSize=500

With wire leads in and out, it cooks down to 8 models from 15 VA to 250 VA.

ak
 
Last edited:

ebp

Joined Feb 8, 2018
2,332
The problem with using a transformer designed for 115 V at nominally 24 V at the same V·A product is that the resistive losses in the windings are likely to make it run very hot, especially when the added issue of high RMS to average current ratio with capacitive filtering is added to the equation.
 

be80be

Joined Jul 5, 2008
2,072
Your using 24 volts to come up with 4 amp that wrong you be lucky to get 2.5 amps from these
the output is figured at peek the same figures used in post 2 to get you a +- 15 volts

4 amps and you'll be seeing this
If a transformer is said to be inherently protected that indicates the transformer is designed in such a way as to protect itself and the load without the addition of any fuse. This is accomplished by designing the unit with high impedance. A non-inherently protected transformer is protected by an internal fuse or circuit breaker. In the instance of an internal fuse it is a one shot fail fuse, so once the fuse trips, the transformer is rendered inoperable. Smaller class 2 transformers of 50VA or less typically do not have fuses or circuit breakers with the circuit as the transformer is designed to prevent overload by failing before the circuit overheats. In essence the VA determines whether the transformer in inherently or non-inherently protected.
I been working with these for over 36 years there and seen 100VA burnout faster then 75 there cheap one's and good ones
They over rate these using 24 volts to do the math
a IC-0100-102 is rated at 4.17 amps on 120 volts it should be 3 amps but I've seen lots fail at less then 3 amps they get hot and short out.
The IC-0100-103 is .83 amps on 120 volts it's a 100VA @ 24 too
I would do some testing with what you have there not all what they say on case.
But good luck with this.
 
Last edited:

Thread Starter

JCapron

Joined Jul 4, 2016
11
Your using 24 volts to come up with 4 amp that wrong you be lucky to get 2.5 amps from these
the output is figured at peek the same figures used in post 2 to get you a +- 15 volts

4 amps and you'll be seeing this

I been working with these for over 36 years there and seen 100VA burnout faster then 75 there cheap one's and good ones
They over rate these using 24 volts to do the math
a IC-0100-102 is rated at 4.17 amps on 120 volts it should be 3 amps but I've seen lots fail at less then 3 amps they get hot and short out.
The IC-0100-103 is .83 amps on 120 volts it's a 100VA @ 24 too
I would do some testing with what you have there not all what they say on case.
But good luck with this.
We must not be buying the cheap ones because we buy several hundred transformers every year with no issues. But thanks for the input.
 

AnalogKid

Joined Aug 1, 2013
11,056
One concern about using a high voltage isolation transformer in a low voltage application is the wire gauge. A 60 VA transformer is designed to deliver approx. 0.5 A at 120 Vac. At 24 Vac, the core easily can shuttle the 30-40 VA needed for this application, but the windings might overheat trying to deliver 1 A. A different solution for this is to use two standard 24 Vac power transformers back-to-back. 24 Vac into the secondary of xfmr #1, #1 120 Vac primary connected to #2 120 Vac primary, #2 24 Vac secondary as the output. Center-taps / dual windings as needed. Twice the iron, probably less total cost, and each winding is designed for the current it is handling. Went there, did that, still working after 40 years.

ak
 

Thread Starter

JCapron

Joined Jul 4, 2016
11
The early (1980's) electronic DDC systems had 24VAC controllers that all came with onboard isolation transformers. They were 300 or 1200 baud TTL devices that were slow but bulletproof. Around the turn of the century, the manufacturers dropped the isolation transformers and switched to RS485. The new controllers were fast but finicky. I just need to find the source for the transformers used in those pre-2000 DDC controllers.
Smart2Xformer.jpg
Thanks for everyone's input.
 
Last edited by a moderator: