Wire in steel pipe vs aluminum pipe

Thread Starter

HighVoltage!

Joined Apr 28, 2014
182
Wondering: If 10A is pushed through a copper wire in steel conduit versus a copper wire inside aluminum conduit, will the steel be more lossier because of it being ferrous and magnetic? Will the conduit heat up more than aluminum?
 

michael8

Joined Jan 11, 2015
472
AC or DC?
Does the return current flow back through the same conduit?
What are the ends of the conduit (electrically) connected to? Does this form a loop?
 

Thread Starter

HighVoltage!

Joined Apr 28, 2014
182
AC or DC?
Does the return current flow back through the same conduit?
What are the ends of the conduit1 (electrically) connected to? Does this form a loop?
AC. The conductor will be shorted and induced with CT to push 10A. Therefore, m each wire will be in a loop. The goal is to start with aluminum and apply same settings to steel to see if it changes. What are your thoughts?
 

nsaspook

Joined Aug 27, 2009
16,250
The NEC usually requires all current carrying conductors of the same circuit to be included in the same cable or conduit.
https://codes.iccsafe.org/s/ISEP201...de-nec-solar-provisions/ISEP2018-NEC-Sec300.3

1697915562650.png
The fields cancel away from the wire pair.

300.20 (B)
Where a single conductor carrying alternating current passes through metal with magnetic properties, the inductive effect shall be minimized by
(1) cutting slots in the metal between the individual holes through which the individual conductors pass or
(2) passing all conductors in the circuit through an insulating wall sufficiently large for all of the conductors of the circuit.

FPN: Because aluminum is not a magnetic metal, there will be no heating due to hysteresis; however, induced currents will be present. They will not be of sufficient magnitude to require grouping of conductors or special treatment in passing conductors through aluminum wall sections.
 

Thread Starter

HighVoltage!

Joined Apr 28, 2014
182
The NEC usually requires all current carrying conductors of the same circuit to be included in the same cable or conduit.
https://codes.iccsafe.org/s/ISEP201...de-nec-solar-provisions/ISEP2018-NEC-Sec300.3

View attachment 305534
The fields cancel away from the wire pair.

300.20 (B)
Where a single conductor carrying alternating current passes through metal with magnetic properties, the inductive effect shall be minimized by
(1) cutting slots in the metal between the individual holes through which the individual conductors pass or
(2) passing all conductors in the circuit through an insulating wall sufficiently large for all of the conductors of the circuit.

FPN: Because aluminum is not a magnetic metal, there will be no heating due to hysteresis; however, induced currents will be present. They will not be of sufficient magnitude to require grouping of conductors or special treatment in passing conductors through aluminum wall sections.
One wire will be in the conduit for this so called experiment. In a magnetic conduit, what actually heats up? The wire itself or conduit due to hysteresis? Therefore, will the ampacity be affected?
 

nsaspook

Joined Aug 27, 2009
16,250
One wire will be in the conduit for this so called experiment. In a magnetic conduit, what actually heats up? The wire itself or conduit due to hysteresis? Therefore, will the ampacity be affected?
Do the experiment, tell us what happens. The NEC has rules for a reason, usually.
 

Thread Starter

HighVoltage!

Joined Apr 28, 2014
182
Do the experiment, tell us what happens. The NEC has rules for a reason, usually.
I will perform! What do you think is going to happen? If I have a wire not inside a conduit, 10A through conductor, and place a steel pipe near it, will the steel pipe heat up? Will there be loses associated to the proximity of steel ferrous pipe?
 

nsaspook

Joined Aug 27, 2009
16,250
I will perform! What do you think is going to happen? If I have a wire not inside a conduit, 10A through conductor, and place a steel pipe near it, will the steel pipe heat up? Will there be loses associated to the proximity of steel ferrous pipe?
Why do you care what I think. The experimental data will show the effects, if any.
 
Last edited:

Thread Starter

HighVoltage!

Joined Apr 28, 2014
182
What do You expect the experiment to demonstrate ???
.
.
.
I just want to see the loses for myself. I would like to see if there are ampacity and heat losses. I would like everyones input on the most efficient way of performing tests to achieving this. I plan on posting results.
 

LowQCab

Joined Nov 6, 2012
5,101
If there were any known, significant losses, there would be readily available
formulas and various online-Calculators to estimate these losses.

Any Inductive or Capacitive, influences or losses, that may be found,
will be so small that they will be very difficult to measure without specialized equipment.

Purely Resistive Wire losses can be estimated using Ohms-Law.
Charts listing Copper-Wire-Resistance for a given length are very common on the Internet.
.
.
.
 

drjohsmith

Joined Dec 13, 2021
1,549
One wire will be in the conduit for this so called experiment. In a magnetic conduit, what actually heats up? The wire itself or conduit due to hysteresis? Therefore, will the ampacity be affected?
Sounds like homework,
What do you think will be the difference if anything
What sort of size effect could you expect ?
How are you going to do the experiment to minimise errors?
Please let us know
 