Voltage Protect 220V split phase? ..#2

Thread Starter

Harph

Joined May 29, 2026
1
I am having a similar issue. I have spider boxes for outdoor stage temporary power distribution using 50 amp California plugs and am concerned of losing the neutral due to bad connections and over voltage the 120 circuits on spider box. Can I use the 3 phase one on a split phase circuit or a pair of single phase with the neutral in series thru them? as I cannot find one for split phase

Mod: link to old thread.
https://forum.allaboutcircuits.com/threads/voltage-protect-220v-split-phase.207143/post-1989902
 
Last edited by a moderator:

MisterBill2

Joined Jan 23, 2018
27,637
CAUTION!!! Neutral conductors should not be series connected !! They should be independent to each outlet point. This reduces the recognized hazard quite a bit.
 