Voltage on neutral line
Dritech
Joined Sep 21, 2011
907
Hi all,
What can be causing voltage on neutral line at a light point when the neutral is disconnected from the distribution box?
Below are the observations done.
NOTE 1: Mains voltage is 230VAC
NOTE 2: With neutral connected, everything works well
With neutral disconnected from DB, with filament bulb connected to light point holder, with light switch on, with all other light switches in the same circuit off:
* Voltage from Neutral to Earth -> 230VAC
* Voltage from Live to Earth -> 230VAC
With neutral disconnected from DB, with LED bulb connected to light point holder, with light switch on, with all other light switches in the same circuit off:
* Voltage from Neutral to Earth -> 160VAC
With neutral disconnected from DB, with LED bulb connected to light point holder, with light switch off, with another light switch in the same circuit on:
* Voltage from Neutral to Earth -> 183VAC
* Voltage from Live to Earth -> 160VAC
With neutral disconnected from DB, with LED bulb disconnected to light point holder, with light switch on, with all other light switches in the same circuit off:
* Voltage from Neutral to Earth -> 0VAC
With neutral disconnected from DB, with LED bulb connected to light point holder, with light switch off, with all other light switches in the same circuit off:
* Voltage from Live to Earth -> 0VAC
38,827
Why do you not expect voltage on neutral when one of switches is ON?
The voltage goes through the ON switch, so I would be surprised if you didn't read a voltage for that condition.
28,331
The voltage you measure from a disconnected neutral to "ground" is dependent on the resistance of your measuring device and the capacitance AND resistance between conductors in all of the connected wiring.
AND GIVEN that a disconnected neutral is defined as an unsafe condition, I ask what is the purpose of this exercise??
Dritech
Joined Sep 21, 2011
907
Hi both, so it is normal to have an LED bulb light up (dim) when neutral is disconnected? Regarding the question why this exercise was done, this actually was not planned :) Is removed the neutral to re-route and forgot to re-connect. When switching on the mains breaker, it noticed the LED which was on from the switch was working, but dim. Also, UNI-T socket tester UT07A was showing all lights on. Shouldn't this show off-green-off?
38,827
There likely is enough capacitance from the floating neutral wire to the ground wire (≈20pF/ft for typical wiring cable with probably about 1-2 feet of wire for every square-foot in you house), to light the LED bulb dimly, since it takes only a small current for that.
MaxHeadRoom
Joined Jul 18, 2013
30,813
When the neutral is disconnected, there is still a circuit path back through earth to the local distribution transformer grounded secondary.
28,331
When the neutral at the distribution panel is opened then the two line sides form a voltage divider that is seldom equal, and the smaller of the loads gets the greater of the voltage, Destruction of items often follows.
38,827
That's if more than one circuit is turned on at the same time, of course.
Dritech
Joined Sep 21, 2011
907
Thanks all for the feedback. So there is noting "abnormal" with the wiring and with the way things were behaving when neutral was disconnected, correct? Also, I still cannot understand why the UNI-T UT07A socket tester was not showing missing neutral (last one from the picture below)
28,331
If another circuit fed from the opposite phase had some load connected between that opposite phase and the internal neutral wiring, enough current could flow to light the indicator between the original line side and the neutral. The voltage would be higher, but the display LED driver would not let that show. If the indicators were NEON bulbs it would have been brighter.
Quite a few years ago I was asked to investigate an outlet in a computer room that had caused a new UPS to smoke. ALL THREE indicators were lighted., A voltmeter check revealed 120 volts between the line and the neutral, and 120 volts between the neutral and the ground, AND ALSO 240 volts between the line and ground.
I chased the problem to a 5KVA Sola constant voltage transformer that fed that outlet via a dedicated circuit. An improperly terminated unused end of the center tapped 240 volt secondary had contacted the bare ground wire inside the transformer terminal enclosure. Because the secondary was completely isolated from all other wiring it did not cause any overload.
Proper termination and insulation of the unused secondary solved the problem.
MaxHeadRoom
Joined Jul 18, 2013
30,813
At one time in the UK, it was forbidden to connect neutral and GND anywhere in the newly wired residence, the GND & N were only connected at the supply transformer neutral.
The GND path resistance had to be measured & conform to a max value res. from installation back to the transformer using the Earth GND & N.
MaxHeadRoom
Joined Jul 18, 2013
30,813
If the N & GND is disconnected at the panel, they are still common to each other by way of the dist. transformer grounded neutral point.