voltage comparison switch

eetech00

Joined Jun 8, 2013
3,961
To clarify the situation:
As Tonyr1084 stated; this is a standard proximity sensor which I expected to output a signal when a ferrous material is close to the end of the sensor (closed state) and output no signal when the ferrous material is removed (open state)
What I am seeing with the sensor is:
VS = input voltage
VO = output voltage
When the sensor is in the Closed State VO= VS.
When the sensor is in the Open State VO= VS-2. I was expecting this to be VO=0
Those measurements indicate the sensor is damaged...

With PNP =on, output should =VS if open collector and no load.
With PNP = off, output should = ~mv, if open collector and no load.
 
Last edited:

eetech00

Joined Jun 8, 2013
3,961
This should work.
When metal is detected (within 8mm), output should be approx +12v
When no metal is detected, output should be ~mV.

1606952847136.png
 
Last edited:

Thread Starter

James Hockney

Joined Oct 23, 2018
19
This should work.
When metal is detected (within 8mm), output should be approx +12v
When no metal is detected, output should be ~mV.

View attachment 223974
Got it to work.
The signal Conditioner (for which there is no datasheet) that it connects into was pulling the Pin 4 Voltage up.
I ended up with a 330 Ohm resistor in the RL position which dropped Pin 4 to 0.3V when the sensor is OPEN and ~12V when CLOSED

Thanks for all the Help.
 

MisterBill2

Joined Jan 23, 2018
18,600
To clarify the situation:
As Tonyr1084 stated; this is a standard proximity sensor which I expected to output a signal when a ferrous material is close to the end of the sensor (closed state) and output no signal when the ferrous material is removed (open state)
What I am seeing with the sensor is:
VS = input voltage
VO = output voltage
When the sensor is in the Closed State VO= VS.
When the sensor is in the Open State VO= VS-2. I was expecting this to be VO=0
SORRY, but that is NOT a STANDARD proximity switch, unless you are using it incorrectly with no load current drawn. And based on the final results this was a correct evaluation. Open collector devices must ALWAYS have a proper load connected in order to function correctly.
 