Using a timer to switch air compressor on and off

Thread Starter

MRENIGMA

Joined Jul 13, 2017
10
Hi

I want to switch an air compressor off from a timer that i have attached the link that i will be using. The compressor is a 3 phase star delta unit and i have attached schematic for it. My question is do i simply put the timer between the coil of the contactor KM1 and use the output of the timer to switch the coil on it or do i have to put it elsewhere in the circuit seeing as it is star delta? The current set up has no timer on it it just has a direct start and stop on it on the front panel on an LCD panel.

http://ie.rs-online.com/web/p/products/8347530/ timeclock
 

Attachments

profbuxton

Joined Feb 21, 2014
421
I can not see how you connect a timer into this system since the start stop control is via the LCD screen. I assume that device controlling this is some sort of PLC with a screen and it controls the starting in Star/ Delta with some sort of program. About the only thing you could do is to start the timer with KM1 and when it times out it would open the emergency stop line. But you would still need to push the start button on screen to start .
Is the contact on terminal 19 a remote start? If it is then maybe that could be used to timer start the cycle?
 

Thread Starter

MRENIGMA

Joined Jul 13, 2017
10
It is being controlled by the controller from the second image in the previous message i sent that is its schematic. it looks like the jumper on terminal 19 is a remote start but the compressor is running non stop so i cant be sure until i can test it. the type of clock i am installing has a relay output so i was thinking if i use the output on the timer to turn on KM1 this would work as everything else is direct on line starting with the star delta
 

MaxHeadRoom

Joined Jul 18, 2013
28,617
Why not replace the PLC input that initiates the start with the output of the timer? AFA I can see you would not use the coil of KM1, this is by passing the controller output.
Max.
 

profbuxton

Joined Feb 21, 2014
421
I don't think just turning on KM1 would work as you need the controller to switch the comp. from Delta to Star at the correct time or load.
I would try the "remote' switch on terminal 19 and see if it starts and stops the machine when operated.
Not sure how you intend to use the timer. How do you want to start the time delay to start and what will reset the timer when timed out.
Had a second close look at what you want to do. You only want to switch comp off after time delay.
Easy. Connect timer coil(timer start) across KM1.Connect timer contact(n/c) in series with emergency contact. When comp starts timer will start, time out and operate emergency stop.When comp stops, timer will be reset for next time. May also be able to use the remote start/stop if that works(preferable).
 

MaxHeadRoom

Joined Jul 18, 2013
28,617
If not a PLC what type of controller is It?
It appears to be some logic controller of some sort.
Do you have a link to the manf.?
Max.
 

MaxHeadRoom

Joined Jul 18, 2013
28,617
It is a form of PLC, seems like an automotive application?
What is it doing in a star-delta starter application?
I imagine there is a timer in there to control the star to delta transfer delay.
Max.
 

WBahn

Joined Mar 31, 2012
29,978
One thing to be sure of is that, however you tackle this, that the compressor head gets unloaded after it is shut down and before it is restarted. Most likely whatever changes you make will not interfere with this process and you'll be fine. Just make sure that you don't inadvertently bypass this process and prevent the head from unloading.
 