UPS transformer question

Thread Starter

skeer

Joined Oct 28, 2022
134
OK so here's the latest measurements, I copied the table outline above. The figures recorded are the most stable during any fluctuations.

blackwhiteblueyellow
black0.60.30.2
white0.60.70.6
blue0.30.70.3
yellow0.20.60.3
 

MisterBill2

Joined Jan 23, 2018
27,508
UNITS?? Are those volts or ohms??
For production transformers the wire sizes for different windings is very common. Even in the cheap junk doorbell transformers, the primary and secondary are different wire sizes.
 

MisterBill2

Joined Jan 23, 2018
27,508
Twp reasons for using voltage readings instead of resistance measurements: First, the no-load voltage reading is an absolute indication of turns ratio,at least in a transformer with no short-circuited turns, and also, because most multi-meters have rather poor resolution for very low resistance measurements. That is verified by the one-digit resistance readings in the supplied table.
For accurate low resistance measurements a four-terminal ohm-meter is usually required.
 

Thread Starter

skeer

Joined Oct 28, 2022
134
Ok here's the requested voltage info, all VAC readings based of a 21.45vac input:

blackwhiteblueyellow
black2.799.1617.09
white2.792.142.42
blue9.162.1416.67
yellow17.092.4216.67
 

KeithWalker

Joined Jul 10, 2017
3,607
UNITS?? Are those volts or ohms??
For production transformers the wire sizes for different windings is very common. Even in the cheap junk doorbell transformers, the primary and secondary are different wire sizes.
I understood that we are trying to figure out the taps on a single primary winding, which should be all the same gauge wire. Mentioning the effect of different gauge wire on different windings is just confusing the issue.
 

Thread Starter

skeer

Joined Oct 28, 2022
134
Which wires were connected to the input, because I can't make any sense of the results?
I don't think I understand.. those VAC values were from a 21.45vac on each of the mentioned primary pairs.

The issues I had was which primary pairs were used for what, and why the blue and yellow leads (in combination with black) cannot accept 120vac without threatening to blow a breaker.

Like this latest set, I can send almost 22 volts to black/yellow but if I try 120 it wants to melt down. Is that perhaps because of that winding having a lower amount of resistance than black/white does?

I feel like I'm not able to verbalize a lot of this to the degree that you guys are used to.
 

Thread Starter

skeer

Joined Oct 28, 2022
134
Do you have a low voltage AC source, lower than 6VAC?
Apply low voltage AC across the secondary winding.
Lower than 6.. no I don't think so. I'll look through my stuff though and make sure. What will a sub-6vac on the secondaries show?
 

KeithWalker

Joined Jul 10, 2017
3,607
The secondary winding will be for charging the batteries, so it will take more than 6V. Connect your 21VAC source across the secondary and then measure the voltages between each pair in the primary. Be careful though, some of the voltages will probably be quite high. Shorting them together could cause damage and touching them could be painful!

Procedure:
1. Connect the AC voltmeter to a pair of wires on the primary.
2. Connect the AC voltage source to the secondary.
3. Record the voltage.
4. Disconnect the AC voltage source from the secondary.
5. Repeat 1 through 4 for every possible pair of wires on the primary..

That will give us the position of the taps on the primary and the voltage ratios between them..
 

Thread Starter

skeer

Joined Oct 28, 2022
134
The secondary winding will be for charging the batteries, so it will take more than 6V. Connect your 21VAC source across the secondary and then measure the voltages between each pair in the primary. Be careful though, some of the voltages will probably be quite high. Shorting them together could cause damage and touching them could be painful!

Procedure:
1. Connect the AC voltmeter to a pair of wires on the primary.
2. Connect the AC voltage source to the secondary.
3. Record the voltage.
4. Disconnect the AC voltage source from the secondary.
5. Repeat 1 through 4 for every possible pair of wires on the primary..

That will give us the position of the taps on the primary and the voltage ratios between them..
Ok here it is, 21.45vac applied to secondary leads:

blackbluewhiteyellow
black40.52134.020.30
blue40.52175.320.29/30
white134.0175.3155.0
yellow20.3020.29/30155.0


The .29/30 signifies a constant fluctuation between the two, and of course all values are in VAC. Back in the day I caught a full T1's 130vdc twice back to back. After the second time my thumb quit working for a while, lol. So I try to be careful after that.
 

MrChips

Joined Oct 2, 2009
34,809
This time the numbers add correctly. I have rounded the numbers in order to keep it simple.
If you treat the input on the secondary as being 20VAC, then divide the numbers shown in the table below by 20 to give the turns ratio with respect to the secondary winding.

For example, blue-yellow is 20:20, blue-black is 40:20, blue-white is 175:20.
White-black is 135:20.

BlueYellowBlackWhite
Blue02040175
Yellow20020155
Black40200135
White1751551350
 

Thread Starter

skeer

Joined Oct 28, 2022
134
Am I understanding correctly, due to the winding size/turns, is why blue/yellow can't handle 120v?
 

MrChips

Joined Oct 2, 2009
34,809
Too few turns means that the inductance is low, which means that the reactance is low.
Reactance of an inductor is calculated using the formula:

XL = 2πfL

where,
XL = reactance (ohm)
f = frequency (Hz)
L = inductance (henry)
 

Thread Starter

skeer

Joined Oct 28, 2022
134
Too few turns means that the inductance is low, which means that the reactance is low.
Reactance of an inductor is calculated using the formula:

XL = 2πfL

where,
XL = reactance (ohm)
f = frequency (Hz)
L = inductance (henry)
Much appreciated!
 