Underloaded Transformer

Thread Starter

sh312

Joined Dec 6, 2014
9
What are the implications if a transformer is underloaded for example

A transformer rated 300kVA but the load it takes is only 220kVA
 

crutschow

Joined Mar 14, 2008
38,503
The only consequence is that the transformer output voltage will be a little higher due to less current through the internal primary and secondary winding resistances.
 

Papabravo

Joined Feb 24, 2006
22,082
Does a little higher mean negligible in this instance. For example if I have 10:1 transformer rated for 5 Amps and I place 120VAC on the primary and draw 1 Amp from the secondary how much does the voltage increase?
 