transformer question

Thread Starter

yoamocuy

Joined Oct 7, 2009
84
1. The problem statement, all variables and given/known data
A single phase 500V/250V transformer that supplies a rated load current of 10 A with a power factor of 0.8 lagging. At no load, the supplied current is 0.25 A with a power factor of 0.10 lagging. I am supposed to find the full-load primary current and express it in polar form. Winding impedance voltage drop can be neglected.


2. Relevant equations
I=Io + I2'
I2'=(N2/N1)*I2
V2/V1=N2/N1


3. The attempt at a solution

Full Load

500V/250V=N1/N2
I think that rated load current is = to I2
therefore, I2'=(250/500)*10 A
I2'=5 A

No Load

Io=0.25 A

using the equation I=Io + I2'
I= 5 A + 0.25 A
I=5.25 A

The correct answer is supposed to be 5.17 A at an angle of -38.9o

I have no idea how to find the angle, and I'm not sure where I went wrong with finding the magnitude of the current. If someone could help me with even just half of the question it would be greatly appreciated.
 

t_n_k

Joined Mar 6, 2009
5,455
Refer the secondary full load current to the primary and add this referred value to the primary no load current (using complex numbers) - then you have the answer. You must use complex addition as the currents are not in phase.
 