Hello, folks. I recently updated all kitchen outlets and two three way switches for a customer. Everything worked fine for three days and then they heard loud ticking noises coming from the circuit breaker in question. The breaker wouldn't trip, but sounded like it was "trying to". Sometimes it would be a loud spark type of TICK, or sometimes it would be a series of tick-tick-tick. They turned the breaker off to stop the TICK or ticking. Then on again and it would starting ticking (or one loud TICK) after about two minutes.
So...I went back yesterday and checked all my wiring on the outlets and everything seemed to be tight and proper.
I exchanged the hot wire from the circuit in question to another breaker and it ticked really loud after two minutes. So it's the line and not the breaker. But I changed the breaker anyway as it was the last of the old ones on the panel (others were already replaced through the years).
Now, here's what I suspect: I had replaced two, three-way hallway light switches (one LED recessed light). When I arrived and was diagnosing yesterday, I noticed they were not working as they should. Turn on Switch A, light turns on. Turn off Switch B, turns off light. Go back to Switch A to turn on and nothing. Go back to Switch B, and I can turn on and off. I checked for line/common wiring at Switch A and of course it was proper. Switch A is the one with the voltage source, BTW.
As I was checking voltage presence at Switch A with a non-contact tester, I hit on a ground wire that beeped for full voltage. I did this a few times and each time it beeped. This was done with the switch only partially out.
Eventually, I pulled the switch out of the box, rechecked (load and runner wires) and everything was proper. I tested the ground again and no beeping. It didn't appear the ground was touching the hot but maybe when I installed it initially it touched it or was really close to it?
Could this be the cause of the problem?
I taped the sides and backs of both switches (not done before) and put them back. I turned on the breakers and no TICK or ticking at all for 20 mins. I tested this three times at 20-25 mins each time and no tripping or TICK. I tested both Switch A and B and now both are totally working three-way style.
One last thing I forgot to mention. I checked all neutrals at the panel and everyone was tight except one: the main thicker neutral coming from MAIN to the bus bar was making contact but loose! Wow. Could this have caused the TICK or ticking? If it did, it's so odd that it would only affect one circuit (although it could be if that one old breaker was weak and on the blitz).
Any helpful insights would be great. The customer will of course update me and I will wait and see for a week or more before I call this a success. But if it doesn't anything else I should look for?
So...I went back yesterday and checked all my wiring on the outlets and everything seemed to be tight and proper.
I exchanged the hot wire from the circuit in question to another breaker and it ticked really loud after two minutes. So it's the line and not the breaker. But I changed the breaker anyway as it was the last of the old ones on the panel (others were already replaced through the years).
Now, here's what I suspect: I had replaced two, three-way hallway light switches (one LED recessed light). When I arrived and was diagnosing yesterday, I noticed they were not working as they should. Turn on Switch A, light turns on. Turn off Switch B, turns off light. Go back to Switch A to turn on and nothing. Go back to Switch B, and I can turn on and off. I checked for line/common wiring at Switch A and of course it was proper. Switch A is the one with the voltage source, BTW.
As I was checking voltage presence at Switch A with a non-contact tester, I hit on a ground wire that beeped for full voltage. I did this a few times and each time it beeped. This was done with the switch only partially out.
Eventually, I pulled the switch out of the box, rechecked (load and runner wires) and everything was proper. I tested the ground again and no beeping. It didn't appear the ground was touching the hot but maybe when I installed it initially it touched it or was really close to it?
Could this be the cause of the problem?
I taped the sides and backs of both switches (not done before) and put them back. I turned on the breakers and no TICK or ticking at all for 20 mins. I tested this three times at 20-25 mins each time and no tripping or TICK. I tested both Switch A and B and now both are totally working three-way style.
One last thing I forgot to mention. I checked all neutrals at the panel and everyone was tight except one: the main thicker neutral coming from MAIN to the bus bar was making contact but loose! Wow. Could this have caused the TICK or ticking? If it did, it's so odd that it would only affect one circuit (although it could be if that one old breaker was weak and on the blitz).
Any helpful insights would be great. The customer will of course update me and I will wait and see for a week or more before I call this a success. But if it doesn't anything else I should look for?
Last edited: