RY Input to Step Down Transformer 230/115 v, Neutral Ground Voltage

Thread Starter

HST20

Joined Jan 1, 2016
3
Hi,
I have a step down transformer which inputs are connected to RY phase of 3 phase 3 wire system.
The outputs of the transformer are COM, 230v & COM, 115v. If i check the voltage between each COM & Voltage,
the voltages are shown correct, but there is voltage difference between two COM terminals about 55v.
Is it normal? or something wrong with the T/F?

and
I am giving 230 v supply from transformer to Motor Drive which has 3 terminals COM, 230v, GND.
the voltage between GND & COM is showing about 55v, recently the drive gone bad,
is this the cause for that?
Neutral to ground supposed to be below 5v but it is showing 55-60v...
 

sailorjoe

Joined Jun 4, 2013
365
Do you have a part number or a datasheet for the transformer? And can you draw a schematic of how you are hooking everything up, please? Helpers need these details to provide accurate help.
 

MaxHeadRoom

Joined Jul 18, 2013
28,688
Normally when a transformer is used, then the secondary is galvanically isolated from the primary so you have lost the earth ground reference, so yes, it is normal to take the neutral to either a new qualified earth point or to the primary service earth conductor if present.
Max.
 

MikeML

Joined Oct 2, 2009
5,444
Measuring voltages between two isolated transformer windings with an AC Voltmeter whose input impedance is =>10MegΩ is bound to read garbage...
 