Reset circuit Help!

Thread Starter

ekremgusani

Joined Mar 20, 2011
157
When i click the A point ON switch button i want the 12v actuator to go from the point A till it touch point B OFF switch and to full stop and the A point ON button switch to reset to OFF, how to do that?
I will appreciate help with circuit explanations.
Thanks.
 

AnalogKid

Joined Aug 1, 2013
12,127
Your question is very difficult to follow. Please post photos of the mechanism, a schematic of the wiring, or *anything* to help us understand what you are talking about. What does this do? What is it for?

ak
 

Thread Starter

ekremgusani

Joined Mar 20, 2011
157
Your question is very difficult to follow. Please post photos of the mechanism, a schematic of the wiring, or *anything* to help us understand what you are talking about. What does this do? What is it for?

ak
I want to make lift cabinet, when I click the power switch ON the cabinet is lifted and when the cabinet is at desired point B, I want the power to reset the actual Point A switch ON to OFF.
I think i need latching relay?
 

mvas

Joined Jun 19, 2017
539
So, you have a Linear Actuator that extends from Point A to Point B ( and I assume - can retract from Point B back to Point A ? )
When you press the "Start" Button the Actuator will turn ON and travel from Point A until it hits a Limit Switch, where it STOPS at Point B ?

How does the Actuator retract from Point B, back to Point A?
a) Do you press the same "Start" Button or
b) Is there a "Extend / Forward" button ( Point A to B ) and a "Retract / Reverse" button ( Point B to A ) ?
 

mvas

Joined Jun 19, 2017
539
Can i just use this latching relay with reset fuction? See link on Amazon
ELECTRONICS-SALON Panel Mount Momentary-Switch/Pulse-Signal Control Latching DPDT Relay Module,12V https://www.amazon.co.uk/dp/B015MSYQ8Q/ref=cm_sw_r_cp_api_i_.ORJCbRAJATDH
Possibly ...
NOTE: The Output Contacts on that Relay are rated for a 8 Amps AC - not DC rating.
How many DC Amps does your DC Motor require?
See the 4th thumbnail down on the Amazon webpage for a typical Forward / Reverse connection ( input side ).
The DPDT Relay Contacts ( output side ) must be wired in SERIES with your Limit Switched to stop the motion, as required.
 

Thread Starter

ekremgusani

Joined Mar 20, 2011
157
Possibly ...
NOTE: The Output Contacts on that Relay are rated for a 8 Amps AC - not DC rating.
How many DC Amps does your DC Motor require?
See the 4th thumbnail down on the Amazon webpage for a typical Forward / Reverse connection ( input side ).
The DPDT Relay Contacts ( output side ) must be wired in SERIES with your Limit Switched to stop the motion, as required.
Have no idea, i just bought it at amazon, here is the link
Walfront DC 12V Linear Actuator 1500N Max Lift 500mm Stroke Electric Motor for Electroic, Medical, Auto Use https://www.amazon.co.uk/dp/B076QDC545/ref=cm_sw_r_cp_api_i_0JTJCbG4PVXJ4
 

mvas

Joined Jun 19, 2017
539
Have no idea, i just bought it at amazon, here is the link
Walfront DC 12V Linear Actuator 1500N Max Lift 500mm Stroke Electric Motor for Electroic, Medical, Auto Use https://www.amazon.co.uk/dp/B076QDC545/ref=cm_sw_r_cp_api_i_0JTJCbG4PVXJ4
I cannot find any Motor data ( amps ) for that Linear Actuator.
But I do not think, that size motor can draw more than 4 or 5 amps.
The Relay Contacts are rated at 8 Amps DC ( per message #10 ), so that looks OK, so far.
Make sure your Limit Switches are rated 8 amps 12 Volt DC.
I believe, the Linear Actuator has built-in Limit Switches that activate at Full Extend and Full Retract.
 

Thread Starter

ekremgusani

Joined Mar 20, 2011
157
I cannot find any Motor data ( amps ) for that Linear Actuator.
But I do not think, that size motor can draw more than 4 or 5 amps.
The Relay Contacts are rated at 8 Amps DC ( per message #10 ), so that looks OK, so far.
Make sure your Limit Switches are rated 8 amps 12 Volt DC.
I believe, the Linear Actuator has built-in Limit Switches that activate at Full Extend and Full Retract.
Thanks
 

Thread Starter

ekremgusani

Joined Mar 20, 2011
157
I cannot find any Motor data ( amps ) for that Linear Actuator.
But I do not think, that size motor can draw more than 4 or 5 amps.
The Relay Contacts are rated at 8 Amps DC ( per message #10 ), so that looks OK, so far.
Make sure your Limit Switches are rated 8 amps 12 Volt DC.
I believe, the Linear Actuator has built-in Limit Switches that activate at Full Extend and Full Retract.
How i can setup it to retract back automatically when full extend is done?
 

mvas

Joined Jun 19, 2017
539
Thank you very much
A thought ... Wire the N.O Contacts of your "Fully Extended / Auto-Reverse" Limit Switch in parallel with your Momentary Reverse Push Button
This will cause the motor to auto-reverse when fully extended.

Design so that the Limit Switch cannot get "crushed" due to forward momentum before reversing.
Make sure your external "Fully Extended / Auto - Reverse" Switch activates before the internal limit switch opens.
 

Thread Starter

ekremgusani

Joined Mar 20, 2011
157
A thought ... Wire the N.O Contacts of your "Fully Extended / Auto-Reverse" Limit Switch in parallel with your Momentary Reverse Push Button
This will cause the motor to auto-reverse when fully extended.

Design so that the Limit Switch cannot get "crushed" due to forward momentum before reversing.
Make sure your external "Fully Extended / Auto - Reverse" Switch activates before the internal limit switch opens.
Can you please draw circuit so i can understand better.
Thanks
 