Question about magnetic contactor in power supply
Kinoton
Joined Jan 20, 2014
52
Hello ,
Ihave an Irem EX85 g xenon lamp power supply. The magnetic contactor has failed three times .Rather than replace it again is it possible (or wise) to simply connect the three phases together via a 500v/100a terminal connector and not use a contactor at all ? I don’t need it to be remotely operated and it can be switched on at the mains . Thanks , Jon
MaxHeadRoom
Joined Jul 18, 2013
30,808
Explain how it failed?, i.e. coil burn out? contact failure?
Generally it is preferable to have a contactor when working with high power 3ph, O/L and rapid turn off capability.
Kinoton
Joined Jan 20, 2014
52
Hi ,
The first time I’m pretty sure the coil burnt out as it was making a loud buzzing sound .Second time there was a thud and then nothing . I can protect the unit with an RCD and hoping I can just directly connect the wires together bypassing the contactor ?
Pyrex
Joined Feb 16, 2022
546
Hello ,
sure you can. What for the contactor is used? For remote control only?
Kinoton
Joined Jan 20, 2014
52
Yes, as far as I can see that’s what it’s intended for . It was designed to be controlled by automation, but this isn’t necessary for me , I can switch it on directly at the 230 v AC mains . Thanks
Kinoton
Joined Jan 20, 2014
52
Hi
28,256
If the contactor coil failed by overheating and burning out, it may have been intended for only intermittent duty, or else the voltage was excessive. Or it may have been an AC coil operated on DC of the same voltage. The model number of the xenon lamp power supply does not tell me the current draw nor any start-up current. How many amps does the supply draw from the mains? And what voltage are the supply mains? AND what is the coil voltage in the application?
Indeed a contactor can often be replaced by a terminal block, a better choice usually will be a suitably rated switch.
MaxHeadRoom
Joined Jul 18, 2013
30,808
If you make changes to your own equipment, in the event of a mishap, it is on you, but if you want to be safe, or others are using it, there are regulations for disconnect in permanently mounted equipment etc
Per NFPA70 & NFPA79.
28,256
The fact is that we know nothing about the application, and if we did not research the model number, we know nothing about the load. In addition, we know nothing about the power that the TS used to operate the contactor. So every response is based on a guess of some kind. Including rules that may not apply at all.
MaxHeadRoom
Joined Jul 18, 2013
30,808
@Kinoton Are you in the UK? I have been out of the loop there for many decades now, so I would suggest checking current/local regs as to what you have and what is required.
Normally not a very good or safe idea to use the main breaker as a switch.
28,256
There are available multi-pole "disconnect " switches in a variety of current ratings. So that is another option that would allow switching the power supply off at it's location. That might be inconvenient, though. We are told it is a xenon lamp power supply, which might include the starting circuit, or maybe not. WE are not even told about the power connection.
Presently I recommend replacing that contactor with an equivalent capacity disconnect switch. Then you have safe local control.
MaxHeadRoom
Joined Jul 18, 2013
30,808
I would be interested in why the contactor coil failed 3 times?, if you just replaced the coil, instead of the whole contactor, one of the symptoms of buzzing, apart from too low coil voltage, is when one of the contactor armature shading rings have opened.
Rare, but does exist.
GetDeviceInfo
Joined Jun 7, 2009
2,284
In my experience, buzzing, chattering relays (that were working) is mostly due to contaminants preventing full armature action. What’s the environment?
28,256
It should be very clear that the failure is most likely due to a mismatch between the coil design voltage and the applied voltage. The TS never mentioned what the connection arrangement was , nor what the specified coil voltage was. So without checking the coil gets connected to the supply voltage, much greater than the specified coil voltage, and the device operates for a while. Then the coil "mysteriously burns out", and so an exact replacement is installed and that one fails as well. The same failure has happened on larger air compressors, where the 120 volt contactor coil was wired across two legs of the 240 volt supply. One day of operation was all it took.
So the very first thing to check will be to verify that the coil voltage applied matches the coil voltage required. Reading those installation instructions is often very important.