Pump Control Reset

Thread Starter

Jay McIntosh

Joined Apr 3, 2019
1
I have an existing circuit which controls a pump motor. A PLC output energizes the control voltage to turn the pump on.
A timing relay allows the motor to start for 10 sec. then opens the circuit.
A flow switch contact is in parallel with the relay contact to hold in the circuit as long a flow is active.
When flow stops, the control circuit is opened.
My problem is that the circuit then tries to restart and the start sequence is initiated again.
How can I add a reset into this circuit, when it has no power until the PLC tells it to start.
 

BR-549

Joined Sep 22, 2013
4,928
You need a low level switch on your fluid reservoir. That switch needs to be in series with pump control relay. We want this switch to open, when reservoir is empty.

Make any sense?
 

BR-549

Joined Sep 22, 2013
4,928
If we knew more about the setup, we might put reservoir condition in the input rung. If it has a reservoir.

It's hard to tell what all it could effect.
 