Problem with diesel genset 50 kw 3 ph 400v 50hz

Thread Starter

ilfish

Joined Jun 10, 2024
32
Have problem with diesel genset 50 kw 3 ph 400v 50hz
AVR good
But no output power
Tip... Rotor slip ring reads 6 ohms
 
Last edited by a moderator:

Ramussons

Joined May 3, 2013
1,567
Check for Reversed Residual Magnetism (RRM)
Disconnect the Field Coil.
Check the output Voltage.
Re Connect the field coil.
Voltage Drop → RRM
How to correct: Flash the Field coil from a 12 volt car Battery a few times. Make sure to use the correct polarity.
RRM will be corrected.
 
Last edited:

MisterBill2

Joined Jan 23, 2018
27,159
Verify the integrity of the rotating field coil circuit. The symptom is no rotating field. It could be a stuck brush. Verifying that the current is correct is a logical diagnostic step.
 