I am having a problem powering a Fan from a control transformer.
The design uses a transformer meant to step down from 240V to 24V. A previous engineer decided to run the 240 to the primary and then use the center tap of the primary to get 120V. So the secondary is not used but the primary is being used. When enrgized this is working. I measure 240-250V range from L1 to L2 and 130V out of the Center Tap. My problem is once I connect a Fan to it i only see 80V from center tap to L1 which is the circuit the Fan is on and the fan is running at a very low speed, but 180V to L2. I feel this is abnormal but is the load from the fan causing the voltage to become that unbalanced? Anyone have an idea on what is causing this or what i can do to stop it. I have already tried using a different fan and the signs are pointing to bad transformer but like i said, with no load it performs how it is intended.
The design uses a transformer meant to step down from 240V to 24V. A previous engineer decided to run the 240 to the primary and then use the center tap of the primary to get 120V. So the secondary is not used but the primary is being used. When enrgized this is working. I measure 240-250V range from L1 to L2 and 130V out of the Center Tap. My problem is once I connect a Fan to it i only see 80V from center tap to L1 which is the circuit the Fan is on and the fan is running at a very low speed, but 180V to L2. I feel this is abnormal but is the load from the fan causing the voltage to become that unbalanced? Anyone have an idea on what is causing this or what i can do to stop it. I have already tried using a different fan and the signs are pointing to bad transformer but like i said, with no load it performs how it is intended.