Power for 3 Phase Y Conn. Load

Thread Starter

jegues

Joined Sep 13, 2010
733
See figure attached for problem statement as well as my attempt.

I'm having trouble finding the power dissapated across the transmission line.

I thought this would be,

\(P_{TL} = \sqrt{3}V_{L}I_{L}cos\phi, \quad \text{Where, } \quad cos\phi \quad \text{is the power factor across the transmission line}\)

Where VL and IL are the line voltage and current across the transmission line.

\(I_{L} = 150 \angle -36.87^{o}\)

\(V_{L} = I_{L} \cdot Z_{TL}\)

Where,

\(Z_{TL} = (2.5 + j10.2) \Omega\)

The solution gets the answer by doing the following,

\(Re \left{ 3 I_{L}^{2} \cdot Z_{TL} \right}\)

Can someone explain my confusion or clarify things?
 

Attachments

t_n_k

Joined Mar 6, 2009
5,455
There are several ways of coming up with an answer but having determined the line current, I would have thought the simplest way of expressing the transmission line power loss would be

\(P_{TL}=3|{I_L}|^2R_{line}\)

or using your values

\(P_{TL}=3*150^2*2.5=56.25kW\)

Sorry that was per phase

it should obviously read

\(P_{TL}=3*150^2*2.5=168.75kW\)

BTW. Your formula would work fine as well provided you convert the voltage drop across the line impedance to a line-to-line equivalent voltage drop.
 
Last edited:

Thread Starter

jegues

Joined Sep 13, 2010
733
There are several ways of coming up with an answer but having determined the line current, I would have thought the simplest way of expressing the transmission line power loss would be

\(P_{TL}=3|{I_L}|^2R_{line}\)

or using your values

\(P_{TL}=3*150^2*2.5=56.25kW\)

Sorry that was per phase

it should obviously read

\(P_{TL}=3*150^2*2.5=168.75kW\)

BTW. Your formula would work fine as well provided you convert the voltage drop across the line impedance to a line-to-line equivalent voltage drop.
Where does your formula come from?

I can see you did P = IV, where V = I/R, but wheres does the 3 infront come from?

Will the math show how it comes about?
 

t_n_k

Joined Mar 6, 2009
5,455
Where does your formula come from?

I can see you did P = IV, where V = I/R, but wheres does the 3 infront come from?

Will the math show how it comes about?
No I didn't use P=IV - rather I used P=I^2R

The RMS magnitude of the current in any line conductor is |I_line|.

This current flows in the line resistance R_line of each of the 3-phase conductors.

So the total power loss in the transmission line for all 3 conductors is

3*|I_line|^2*R_line

The phase angle of the current doesn't matter in this approach since current and voltage in the line resistances (as lumped elements) are always in phase.
 