Power factor tips
inwo
Joined Nov 7, 2013
2,419
We have a city waste water treatment plant in our tiny city, paying a large penalty for a pf of 59%.
Plant was federal project with all the overkill redundancy and intrinsically safe sensor circuitry.
Only 6 years old. Most all motor load is on vfds.
Most everything works well. I've been called a dozen times or so for repairs.
Where would I start looking for the low hanging fruit?
My knowledge predates vfds.
My meter doesn't do harmonics. thd
Will I need to update my equipment to even get a sense of what's going on?
My wife is in charge of another building in town. Library. After obtaining a grant for an updated AC system, she was taking heat for utility bill. 83% in her building. Only two suspects there. Compressor load and lighting.
I believe the city should look into the treatment plant first.
Is my assumption of vfds having good pf wrong?
30,795
VFD's can be the culprits, the service supplier here will bring in a team to assess and record the P.F. and recommend suitable Capacitor correction.
inwo
Joined Nov 7, 2013
2,419
That was my first suggestion to the city.:confused:
Back in the day, I worked for a contractor when pf correction was just becoming popular. We just had the power company give us the recommendations. Just as you suggest.
My wife, and city, claims they (power company) have no interest in helping.:(
Their suggestion is to call a contractor.
I am an electrical contractor (licensed in the state), but have no recent knowledge when vfds are in the mix.
The city doesn't understand the savings potential. I don't have the confidence or experience to guaranty results.
Can you explain in general terms how the vfds with capacitor input power supply busses lead to poor pf?
Understand the effect on thd but not how this relates to pf problem.
I asked if penalty was for distortion and was told it is specifically for pf.
inwo
Joined Nov 7, 2013
2,419
What about a meter suggestion to localize the problem?
All I have is an amprobe acd-30p.
http://content.amprobe.com/DataSheets/ACD30P.pdf
Without thd.:(
I remember a job a while back. My fluke was reading over 600vac upstream 50' from a small 10hp vfd. (480 volt system)
Special meter or filtering must be required.
As general practice, I use input reactors on my jobs.
Haven't checked yet, but don't remember seeing them on this job.
studiot
Joined Nov 9, 2007
4,998
Options
Read the technical press
http://www.waset.org/journals/waset/v78/v78-344.pdf
Get a specialist contractor in
http://www.sml.ltd.uk/power_factor_correction.html
Do it yourself - work it out from the texbook
http://books.google.co.uk/books?id=...factor correction in pumping stations&f=false
One suggestion, however, most pumping stations have some redundancy so you can take measurements / experiment on some plant that is offline for maintenance.
Look also at the type of motor. If you have the old slow moving type spreader bars in the treatment system their motors can be inefficient.
Is there any UV treatment involved? The UV generator probably has an opposite phase PF to the motors.
GopherT
Joined Nov 23, 2012
8,009
The problem may not be the big VFDs. Look for lightly loaded induction motors in air handling or pumps - especially if the are running under no load conditions. The post above says waste plants rotate demand through different sections. If so, do any pump motors or blowers continue to run with no load?
See this document from ABB claiming that FVDs prevent the need for PF.
here
Especially the note in the last paragraph.
inwo
Joined Nov 7, 2013
2,419
The problem may not be the big VFDs....True from what I read....... Look for lightly loaded induction motors in air handling or pumps - especially if the are running under no load conditions. The post above says waste plants rotate demand through different sections...very small plant... If so, do any pump motors or blowers continue to run with no load?......modern designed, automated plant with mostly vfds. I'll check
See this document from ABB claiming that FVDs prevent the need for PF..........I'm puzzled
here
Again, this is why I'm puzzled. All except two motors are are on vfds now.
I've been under the assumption that one advantage of vfds is better pf.
I guess I'll start with those.
30,795
Can you explain or link?
I phoned a couple of contacts I have who are engineers that are with the service provider, and they say it is not so much P.F. that is a problem but Electrical noise from VFD's.
In the past I have usually used 3ph chokes either just on the motor side and in some case input and output.
inwo
Joined Nov 7, 2013
2,419
That's what my research led me to believe.
The pf problem then, still eludes me, as the cities cost penalty is for pf not harmonics. Unless I've been given false information.
As in previous post. I also use input reactors. Just as "good practice". Output reactors are specialized and only required on long runs, I believe.
ps.
Your contacts didn't hint that they monitor and penalize for noise did they?
GopherT
Joined Nov 23, 2012
8,009
A lot to digest.
Mostly things I've found in my searches.
An explanation for poor pf on vfd systems doesn't jump out.
Think I will concentrate on the non-vfd loads first as I don't have proper equipment for the others.
That is the best plan from my point of view.
GetDeviceInfo
Joined Jun 7, 2009
2,284
here
Excellent article and worth the full read. Pat attention to the comments about lightly loading, as this applies to transformers as we'll. I'd get out the single line drawings to map out a strategy. Request your annual usage data from the utility as they likely have hour by hour usage with pf. Compare that with plant loading.