metal oxide varistor

Thread Starter

paprider

Joined Jun 23, 2015
5
Can anyone explain on what basis Vsiov has been calculated using the equation Vsiov=1000x 0.9/1.1. I need to use an MOV from EPCOS S14 series to satisfy surge conditions as per IEC 61000-4-5. I have attached a snapshot of the calculation.
 

Attachments

Nick Bacon

Joined Nov 7, 2016
130
I have been looking into the same as you for my project. As far as I can see the MOV should be approx 20% above supply voltage. I think I have settled on 300V. I believe the air discharge test is now 8kv (lightening strike protection) but may be for your application it is 4kv.