This project takes place in a kitchen. Existing under-cabinet LED strips totalling 16W are fed by a 24v driver rated at 28.8W, 1.2A. I need to add a ceiling mounted LED spotlight to this circuit. Technically I have “room” for a 12W LED. (28.8 - 16 = 12.8). But I figure this might be pushing it as I’d be running the driver at 97% of its rated capacity. So I bought a 24V, 9W LED on AliExpress. When installed it seems really dim. So I connected my VOM in series and got a reading of 157ma. This would mean it’s drawing 3.8W instead of the rated 9W — which might explain why it’s dim. I assume it’s been mislabelled. Or is it incorrect to measure LED current as if it were a resistive load? (No dimmer is involved.)