like to know some basic of wiring 230/460vac machine to wall power of 600v.

Thread Starter

LAOADAM

Joined Nov 21, 2018
956
Hi all.
what's the basic work steps to do and middle supplies need prepare?

declaration:I'd just like to know some thing, won't do any danger stuff.

Thanks
Adam
 

MaxHeadRoom

Joined Jul 18, 2013
30,557
Much more info needed in order to assist!
What/where is the 600v supply coming from?
If this from the service Co. then sounds like you are also located in Canada ?
What is the equipment?
Sounds like you require a transformer?
oops I see you mentioned DC !
 

MaxHeadRoom

Joined Jul 18, 2013
30,557
If you are using the 3ph 600v wall power. How is the 600v delivered, what is the current demand of the system?
Much more info need than two lines of a OP !!
 

Thread Starter

LAOADAM

Joined Nov 21, 2018
956
Much more info needed in order to assist!
What/where is the 600v supply coming from?
If this from the service Co. then sounds like you are also located in Canada ?
What is the equipment?
Sounds like you require a transformer?
oops I see you mentioned DC !
Thanks.
I modified that: ac; sorry.
the 600v box existing on the unit wall;
in Canada;
Lathe machine;
30HP;
 

panic mode

Joined Oct 10, 2011
4,864
i saw the same but find it suspicious that DC would have those exact levels... those are common voltage levels for AC.

EDIT... so it was AC... then you need to know if this is single or three phase and what power. with that you can choose suitable transformer. can you post nameplate of the lathe?
 

Thread Starter

LAOADAM

Joined Nov 21, 2018
956
i saw the same but find it suspicious that DC would have those exact levels... those are common voltage levels for AC.

EDIT... so it was AC... then you need to know if this is single or three phase and what power. with that you can choose suitable transformer. can you post nameplate of the lathe?
yes, three phase.
the machine doesn't buy yet, like to know how much auxiliary work will be.
also, saw the shop unit mostly equipped 600vac box (transform?), why?
Thanks
 

panic mode

Joined Oct 10, 2011
4,864
well... the actual voltage is based on national standard....
when it comes to 3phases:
most of the world uses 400V
parts of Brazil use 440V
the US uses 460V (or 480V) or sometimes 230V (or 240V).
in Canada that is 575V phase to phase... (or 600V).

so if you are in Canada, yes, your facility will normally be fed by 600V. but often one would add transformers to be able to use US machines for example. so transformers that step down from 600V to 240V or 480V are very common.
1725305353322.png

https://documents.hammondpowersolut...nfo/HPS-Standard-Product-Catalog-(HTP-16).pdf
 
Last edited:

MaxHeadRoom

Joined Jul 18, 2013
30,557
So you are faced with a problem that has repeatedly existed, US machines imported to Canada!.
600v is a Canadian standard supply voltage.
If a 230/440 machine tool then it is going to be 3ph most likely.
You are having to either convert the m/c or have a 600v -460 transformer installed.
 

Thread Starter

LAOADAM

Joined Nov 21, 2018
956
well... the actual voltage is based on national standard....
when it comes to 3phases:
most of the world uses 400V
parts of Brazil use 440V
the US uses 460V (or 480V) or sometimes 230V (or 240V).
in Canada that is 575V phase to phase... (or 600V).

so if you are in Canada, yes, your facility will normally be fed by 600V. but often one would add transformers to be able to use US machines for example. so transformers that step down from 600V to 240V or 480V are very common.

https://www.automationdirect.com/ad...MIsq65i_6kiAMVHjbUAR1-ZzmNEAAYAiAAEgKLzvD_BwE
can I just use the 3ph 600v's line voltage of 400V L-N? be able to run but lower the capacity?
 

Thread Starter

LAOADAM

Joined Nov 21, 2018
956
So you are faced with a problem that has repeatedly existed, US machines imported to Canada!.
600v is a Canadian standard supply voltage.
If a 230/440 machine tool then it is going to be 3ph most likely.
You are having to either convert the m/c or have a 600v -460 transformer installed.
Thanks.
'either convert the m/c or have a 600v -460 transformer installed'.
this is exactly what my confusion now.
 

panic mode

Joined Oct 10, 2011
4,864
nope...do not connect 400VAC load to 600VAC mains. that is a sure way to destroy things.
increasing supply voltage also increases current... (so delivered power is a square function).
converting machines is costly and requires skill that you do not have.
selecting correct transformer is much simpler.

btw. it is not necessary to get individual transformer for each piece of equipment. one transformer (correctly sized) could power many machines.
 

Thread Starter

LAOADAM

Joined Nov 21, 2018
956
nope...do not connect 400VAC load to 600VAC mains. that is a sure way to destroy things.
increasing supply voltage also increases current... (so delivered power is a square function).
converting machines is costly and requires skill that you do not have.
selecting correct transformer is much simpler.

btw. it is not necessary to get individual transformer for each piece of equipment. one transformer (correctly sized) could power many machines.
Thanks.
'nope...do not connect 400VAC load to 600VAC mains.' knowledge like this is valuable for me.
I'll check if there is an existing transformer.

can do any thing easy with 230vac 3ph?
if there have 220v (not sure yet) ?
 
Last edited:

panic mode

Joined Oct 10, 2011
4,864
and that is why i mentioned to not even think about converting machine... Basic lathe may be a simple machine but modern ones are not. In general there is more to it than you want to know... and i have yet to see where this is a more economical option. but that is ok if you need science project and don't mind hiring engineering service.

if the equipment is UL approved (anything out of US should be) and you are just adding transformer, you still need field inspection for the installation but only for the transformer, not the machine.

but when you are to modify equipment, any approval of the machine would be void. then the machine itself would need to go through CSA inspection. and depending on what you get there (and who the inspector is) this can be quite expensive (practically always is) because then you would also need to worry about bunch of other things that are not yet on your radar... like SCCR rating... but that practically goes away if load (your machine) is behind transformer since transformer acts as a bottleneck for fault currents.

on the other hand selecting transformer is pretty straight forward.... just need to match few things:
1. the primary voltage (we already know it is 600V)
2. the secondary voltage (480V for example)
3. power (must be sufficient for rated load but normally one can also use higher power if needed)
4. correct environmental protection... in most shops transformer could be air wented, specially when mounted on the wall so debris cannot get to it (dust, water, metal chips, whatever).
5. add 600V fused disconnect (this can be bought cheap from any electrical supplier and will meet the standards, Eaton or whoever).
6. any licensed electrician can wire it (use correct taps, ground secondary,...)
7. get field inspector (ESA/CSA/Entela/QPS/...) to bless it and apply sticker.

1725308608543.png1725308685822.png
 
Last edited:

MaxHeadRoom

Joined Jul 18, 2013
30,557
What HP are the motors? and rating of the machine?
In some rare cases it can be economical to convert to lower voltage or even 1ph
e.g. Servo's often are 1ph fed, lower voltage.
Spindle motor changed. It is often suprising how much can be 120v or 240 on a machine tool.
So IOW, determine the main reason or section requiring 440v.
I have done this on the odd occasion,
Try and get more info on the machine design and ratings.
Obtain the VA rating.
Oops, I see 30HP spindle! :oops:
 

MaxHeadRoom

Joined Jul 18, 2013
30,557
Another question if CNC!
Is this a brand new machine, or is used? purchased by auction or shop sale?
The reason I ask is, I have been contacted a few times over the years, where those that have purchased used machinery in auctions or shop-closing sales etc.
When purchased, it is often overlooked to ask for the copy of machine parameters. which are generally battery backed up in the machine. and when in the event that the parameters have to be re-loaded, and the back up material is missing, the machine is dead in the water!
If this is a CNC M/C from a reputable manuf. they are often available on file.
But in the case of an individual retrofitter, or from a Co. now deceased, the M/C reverts back to a lump of iron without them! o_O
It costs a considerable amount for myself or someone, to reverse-engineer and restore the M/C to its working condition!
 

MisterBill2

Joined Jan 23, 2018
27,164
Hi all.
what's the basic work steps to do and middle supplies need prepare?

declaration:I'd just like to know some thing, won't do any danger stuff.

Thanks
Adam
The most important beginning work step is a means to assure that the power stays OFF until all of the workers are clear of all the conductors.
 

MaxHeadRoom

Joined Jul 18, 2013
30,557
Any supply installation has to be inspected to ensure covered by the local Electrical code. CEC etc. And licensed personnel
P.S. The OP has not been back since the original post! :oops:
 

MisterBill2

Joined Jan 23, 2018
27,164
In my area being licensed means having paid quite a few hundreds of dollars to the local city hall bunch, and having a fair idea as to what you are doing. It does not by any standard require serious competence.
 

Thread Starter

LAOADAM

Joined Nov 21, 2018
956
and that is why i mentioned to not even think about converting machine... Basic lathe may be a simple machine but modern ones are not. In general there is more to it than you want to know... and i have yet to see where this is a more economical option. but that is ok if you need science project and don't mind hiring engineering service.

if the equipment is UL approved (anything out of US should be) and you are just adding transformer, you still need field inspection for the installation but only for the transformer, not the machine.

but when you are to modify equipment, any approval of the machine would be void. then the machine itself would need to go through CSA inspection. and depending on what you get there (and who the inspector is) this can be quite expensive (practically always is) because then you would also need to worry about bunch of other things that are not yet on your radar... like SCCR rating... but that practically goes away if load (your machine) is behind transformer since transformer acts as a bottleneck for fault currents.

on the other hand selecting transformer is pretty straight forward.... just need to match few things:
1. the primary voltage (we already know it is 600V)
2. the secondary voltage (480V for example)
3. power (must be sufficient for rated load but normally one can also use higher power if needed)
4. correct environmental protection... in most shops transformer could be air wented, specially when mounted on the wall so debris cannot get to it (dust, water, metal chips, whatever).
5. add 600V fused disconnect (this can be bought cheap from any electrical supplier and will meet the standards, Eaton or whoever).
6. any licensed electrician can wire it (use correct taps, ground secondary,...)
7. get field inspector (ESA/CSA/Entela/QPS/...) to bless it and apply sticker.